ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Updated Forum Software
by Admin - 06/15/21 10:23 AM
Broken Outlet & Dangling Light
by LoneWolf - 06/14/21 08:21 PM
How's all our Non-US folks doing?
by C-H - 06/14/21 05:42 PM
Where is Everyone?
by Bill Addiss - 06/14/21 12:37 PM
Conduit over Vinyl Siding
by Bill Addiss - 06/14/21 12:35 PM
New in the Gallery:
2020 - 2021 Winter Project
2020 - 2021 Winter Project
by Bill Addiss, April 29
Garden 2021
Garden 2021
by Bill Addiss, April 26
Who's Online Now
1 members (Scott35), 6 guests, and 17 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#88886 08/04/04 08:51 PM
Joined: Jun 2004
Posts: 613
S
Member
Can someone please tell me which article in the code covers the use of flex...sometimes called greenfield.I use the 3/8 size for hooking up pumps and relays on residential boilers. Am I required to use anti-shorts sometimes called redheads with flex and where does it state this in the code if so required.Also is there a restriction in the length that can be used.And is a grounding conductor required to be installed in lengths over 6 feet???An associate said if we had to use anti-shorts they would come with the roll of flex when purchased like with BX and MC cables.I always use redheads anyway but couldn't find it in the code book.

2017 / 2014 NEC & Related Books and Study Guides
#88887 08/04/04 09:09 PM
Joined: Feb 2002
Posts: 840
C
Member
To my knowledge, anti shorts are not required for anything other than Type AC (BX) cable.


Peter
#88888 08/04/04 09:09 PM
Joined: Nov 2003
Posts: 269
E
Member
Article 348 covers type FMC or "flex". There is no requirement to use the anti-short bushings. It is a matter of choice.


John
#88889 08/06/04 09:22 AM
Joined: Apr 2004
Posts: 156
R
Member
My company requires them to be used. We build HVAC&R equipment that can have high vibration levels. There isn't a specification to use them other than the fact that it enhances protection and can save alot of money as opposed to leaving them off and shorting out the equipment. Case in point a unit cooling an office in Arizona in August. Greenfield not tightened enough, conduit slips out and vibrates a hole right through the wire. Trips the compressor out and no air-conditioning. Alot of griping and litigation threats for what the cost of a simple cheap protector could have saved.

Look at Article 350 for Flexible Metal Conduit (Greenfield). Read the Grounding section carefully. Like Liquidtight you have to read through the exceptions and the requirements ten times to get the jist of it.

The reference to 250-118 will nock out the use of conduit for grounding in a heartbeat if you don't meet the requirements. We have recently been arguing this same problem with Liquidtight and I told the guys on the floor to run a ground wire and put that dog to bed. Without the wire there is the need to have fittings and conduit rated for grounding and that if the flex is needed for flexibility you need the ground wire anyway. That way if you didn't put in enough to flex and the conduit gets pulled out you will still have an effective ground. (And if you use redheads you probably will save a short circuit problem.)

You can search for grounding in the forum and have plenty to read for the rest of the week. Always remember that the care you take to make the product safe is just as valuable as making the product work.

Robert

#88890 08/06/04 04:20 PM
Joined: May 2004
Posts: 162
C
Member
The Code uses the phrase "insulating bushing or its equivalent protection shall be provided between the conductors and the armor". For type AC (as previously mentioned)See section 320.40

3/8" FMC is addressed in Article 348 of the NEC.Conductor fill is covered in Table 348.22 make note as to whether you are using connectors that are internal or external.

Grounding requirements are covered in 348.60 Where used to connect equipment where flexibility is required, an equipment grounding conductor shall be installed. If you install one it counts as conductor fill.

Also Article 250.118 recognizes FMC as an equipment grounding means if the conduit and the fittings are listed as such. Or you could be useing FMC that is listed, but not listed as a grounding means(and it’s probably not) under the following conditions. The total length (return path) is not greater than 6 feet, the fittings are listed for the purpose (few check), and the conductors are protected at 20 A or less. Of course it can not be installed to provide flexibility, and function as a EGC.

Note that section 348.42 does not mention insulating bushings. But then again the NEC is only a minimum standard!

[This message has been edited by cpal (edited 08-06-2004).]

[This message has been edited by cpal (edited 08-06-2004).]


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
akmaster
akmaster
alaska
Posts: 74
Joined: June 2012
Top Posters(30 Days)
Admin 14
Trumpy 10
Popular Topics(Views)
280,390 Are you busy
213,461 Re: Forum
200,378 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5