Joined: Apr 2002
Posts: 178
R
Member
Is it permissable to knock out a 2" hole near the top side of a outdoor panel?Plans are to knock out a 2" hole about 4" down from top on the left hand side and also knock a hole in the meter can to match so they will be even(appearance)Co-worker says no but we can`t find in nec.And also can I use pvc nipple or would it have to be water tight hub?

2017 / 2014 NEC & Related Books and Study Guides
Joined: May 2004
Posts: 162
C
Member
There is a product on the market refered to as a "myers hub" or possibly a sealing type locknut

check this site out also http://www.electrician.com/articles/myers.htm
http://www.electricaldeals.com/html/search.php3?column=AllenNum&search=MYER&source=ovr this site has an illistration of a hub

If you install two one on the meter and the other at the panel I don't see a proble interconnecting with PVC (two male adapters and a nipple to fit)

charlie P

312.2 Damp, Wet, or Hazardous (Classified) Locations.
(A) Damp and Wet Locations. In damp or wet locations, surface-type enclosures within the scope of this article shall be placed or equipped so as to prevent moisture or water from entering and accumulating within the cabinet or cutout box, and shall be mounted so there is at least 6 mm (ΒΌ in.) airspace between the enclosure and the wall or other supporting surface. Enclosures installed in wet locations shall be weatherproof.
Exception: Nonmetallic enclosures shall be permitted to be installed without the airspace on a concrete, masonry, tile, or similar surface.

Joined: Apr 2002
Posts: 2,527
B
Moderator
If a field-cut KO in a NEMA-3R enclosure wall is partially or completely above the elevation of factory KOs, a hub is most often in order.

The other concern is preservation of wire-bending space.

Joined: Jul 2004
Posts: 41
N
Member
You can also use a sealing locknut and do what you are talking about doing.


Kenny Wilee

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Niko
Niko
Campbell, CA
Posts: 356
Joined: August 2006
Top Posters(30 Days)
Admin 14
Trumpy 10
Popular Topics(Views)
280,390 Are you busy
213,461 Re: Forum
200,378 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5