#88831 08/02/04 09:10 PM
Joined: Jun 2004
Posts: 613
S
Member
We set up a residential kitchen for an electric cooktop by running a 8-3 romex to the kitchen.The owner got a "Melie" cooktop which is 3 seperate units each rated at 2.8 KW ...mounted side by side only 30inches wide each with its own seperate flex wipp with 12 gauge wire in the flex. Can all 3 be connected to the 8-3 romex that we installed and protect them with a 40 amp breaker???

2017 / 2014 NEC & Related Books and Study Guides
#88832 08/03/04 01:26 PM
Joined: Nov 2003
Posts: 269
E
Member
Yes. See 210.19(A)(3)exception 1.


John
#88833 08/03/04 08:49 PM
Joined: Jun 2004
Posts: 613
S
Member
Thanx electricman2!!!

shortcircuit


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Top Posters(30 Days)
Admin 14
Trumpy 10
Popular Topics(Views)
280,409 Are you busy
213,479 Re: Forum
200,389 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5