Low voltage transformer??? Why??? #8867 04/07/02 11:34 PM
Joined: Jun 2001
Posts: 161
M
Mike Wescoatt Offline OP
Member
Are there any advantages of using a 480-208/120 transformer versus a 7200 or 12470 volt primary transformer??? We're looking at a couple of 150KVA type K and about six 200KVA 208/120v standard xfmr's. Wouldn't the 12.47KV primary xfmr deal with load changes better than the 480V xfmr? Also, we would be able to cut down on supply amperage and physical size of the package with 12.47KV vs. 480v, right? Any thoughts??


Mike Wescoatt
Work Gear for Electricians and the Trades
Re: Low voltage transformer??? Why??? #8868 04/08/02 07:20 AM
Joined: Mar 2001
Posts: 2,056
R
Redsy Offline
Member
Are you wondering about the advantages of the utility supplying a high-tension (primary) service versus a 480 volt supply?

Re: Low voltage transformer??? Why??? #8869 04/08/02 09:27 AM
Joined: Mar 2002
Posts: 31
S
smurf Offline
Member
Won't the utility co. supply your x-formers? If so, they determine what size according to your load needs. You can ask for a certain secondary voltage.

Re: Low voltage transformer??? Why??? #8870 04/08/02 10:03 AM
Joined: Mar 2002
Posts: 582
R
Ron Offline
Member
Generally medium voltage (7kV or 13kV) service is better than low voltage (480V) for voltage drop, capacity and reduced conductor size.
You need to consider who will be servicing the transformer (on site personnel/electrician, a third party electrician or the utility.
Clearance and construction requirements help delineate installation differences.


Ron
Re: Low voltage transformer??? Why??? #8871 04/09/02 11:55 AM
Joined: Jun 2001
Posts: 161
M
Mike Wescoatt Offline OP
Member
This will be in a refurb of a hotel showroom where the 480 is already existing. They keep on saying that they're strapped for supply already in this area. I was thinking we should pull a 12.47KV line to a distribution to deal with the 8-10 xfmrs we will need, but they want to keep the old 480V lines... Perhaps if it was 10,000A service...


Mike Wescoatt
Re: Low voltage transformer??? Why??? #8872 04/09/02 04:58 PM
Joined: Dec 2000
Posts: 127
G
gpowellpec Offline
Member
Who will supply and maintain the transformer? With deregualtion in Texas the customer would. Have you investigated the cost of going from a 480 voltage insulation rating to 12.47 kv? It seems the utility company would like to supply at the higher voltage (especially if the customer owns the transformer)because the losses on their side of the meter would be less.

Re: Low voltage transformer??? Why??? #8873 04/09/02 06:36 PM
Joined: Dec 2000
Posts: 4,283
electure Offline
Member
How large an installation are you talking about (in additional load)?
There are big differences here.
You'd better be in the planning stages of this job?



[This message has been edited by electure (edited 04-09-2002).]

Re: Low voltage transformer??? Why??? #8874 04/11/02 09:49 PM
Joined: Jun 2001
Posts: 161
M
Mike Wescoatt Offline OP
Member
All of the equipment will be customer owned and serviced by onsite Engineering department. We're still trying to come up with load sheets because we're in the early planning stages... We know the dimming system will need 208/120 700KVA service


Mike Wescoatt
Re: Low voltage transformer??? Why??? #8875 04/11/02 10:02 PM
Joined: Mar 2002
Posts: 582
R
Ron Offline
Member
Is that a typo, or is the lighting dimming system need 2000 amps of capacity?


Ron
Re: Low voltage transformer??? Why??? #8876 04/11/02 11:45 PM
Joined: Oct 2000
Posts: 2,721
Scott35 Offline
Broom Pusher and
Member
Sounds to me that you are describing the typical "Customer Owned SDS" [Separately Derived System].

The Customer is supplied with a 480Y/277 VAC 3 Phase 4 wire system of -X- KVA [or MVA].

If the load calced was higher than what can be derived from a 480 VAC service, then this would have [or should have] been supplied by a 2400 VAC system, or a 4160 VAC system.

The Utility supplied Power System will be in respect to the Calculated Load. That's where the System Voltage becomes a factor.

Scott SET.


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
RH1
RH1
California
Posts: 22
Joined: August 2009
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 8
NORCAL 3
Popular Topics(Views)
269,957 Are you busy
204,381 Re: Forum
192,599 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3