30 Hp with V.F.D. 430.6 & 430.150 30 hp =40amps at 460 volts 40x150%=60amps wire size=3#6s &1#10 Disconnect Switch=60amp Should disconnect switch be up sized to 100 amp (fuseable).Seems to be hitting it right on the mark? wondered if maybe to close??
75hp 460v 3 phase (96 amps) 96x150%=144 amps wire size=3#1s&1#8 Disconnect switch =100amps
Hows it look guys don;t have into off name plates of VFD so using 430.6c
|
|
|
|
|
Joined: Mar 2003
Posts: 849
OP
Member
|
Opps Disconnect switch 150 amps not 100 amps
|
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
Take a look at 430.2.
I do not see an option for using the tables as far as the VFD is concerned.
[This message has been edited by iwire (edited 07-02-2004).]
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
|
Joined: Mar 2003
Posts: 849
OP
Member
|
430.6c If the maximum operating current does not appear on the nameplate ,the ampacity determinated shall be based on 150% of the valves given in tables 430.149 and 430.150.
|
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
I do not see that 430.6(C) changes the requirments of 430.2
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|