GFCI #88312 05/27/04 09:47 PM
Joined: Mar 2004
Posts: 26
T
texassparky Offline OP
Member
When installing outlets in the soffit of a home for Christmas lighting do these plugs need to be gfi protected? I have always put in a gfi breakers but was told that they didnt have to because they where over 7' off the ground. I feel better about them having protection, you can never be to carefull.

2017 / 2014 NEC & Related Books and Study Guides
Re: GFCI #88313 05/27/04 10:10 PM
Joined: Aug 2003
Posts: 1,374
R
Ryan_J Offline
Moderator
GFCI required.


Ryan Jackson,
Salt Lake City
Re: GFCI #88314 05/27/04 10:17 PM
Joined: Mar 2004
Posts: 26
T
texassparky Offline OP
Member
Thanks Ryan. Could you tell me where I could find this in the code book.

Re: GFCI #88315 05/27/04 10:26 PM
Joined: Aug 2003
Posts: 1,374
R
Ryan_J Offline
Moderator
210.8(A)


Ryan Jackson,
Salt Lake City
Re: GFCI #88316 05/28/04 12:10 AM
Joined: Feb 2004
Posts: 75
S
scameron81 Offline
Member
I was always under the impression that they didn't have to be GFCI because of the
210.8(A)(3) exception that allows for non GFCI on plugs that are not readily accessible.

Re: GFCI #88317 05/28/04 01:23 AM
Joined: Apr 2002
Posts: 558
C
caselec Offline
Member
The exception to 210.8(A)(3) only applies to receptacles used for snow-melting & deicing equipment.

I guess Christmas lights would help melt the snow and ice. [Linked Image]


Curt Swartz
Re: GFCI #88318 05/28/04 08:03 AM
Joined: Aug 2003
Posts: 1,374
R
Ryan_J Offline
Moderator
I hoping I wasn't wrong, since I didn't have my code book. I really should stop winging it like that [Linked Image]


Ryan Jackson,
Salt Lake City
Re: GFCI #88319 05/28/04 02:11 PM
Joined: Apr 2003
Posts: 139
B
BPHgravity Offline
Member
There was a local contractor that was installing receptacles in the soffit for Christmas lighting and was also trying to use the snow-melting and deicing equipment exception. That would be fine except we are in South West Florida. It did snow here once about 2,000 years ago!!!


Bryan P. Holland, ECO.
Secretary - IAEI Florida Chapter
Re: GFCI #88320 05/28/04 04:19 PM
Joined: Aug 2003
Posts: 1,374
R
Ryan_J Offline
Moderator
I don't know what that exception would save you, since you would then have to have GFPE. Is GFPE cheaper? I thought it was more.

[This message has been edited by Ryan_J (edited 05-28-2004).]


Ryan Jackson,
Salt Lake City

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Potseal
Potseal
Saskatchewan
Posts: 264
Joined: February 2013
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 20
Popular Topics(Views)
272,206 Are you busy
206,091 Re: Forum
194,097 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3