Member
OK ,I have a 200amp service residential.I have a out building/workshop with a 100 amp main breaker panel installed. Now can I run 3 wire service to it?Bond neutral to can.
Do I place a rod there or not?
Do I run 4 wire and place rod?
I re read some past threads but need alittle
reassurance.Thanks in advance.
using direct burial cable pvc conduit.

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

Joined: Aug 2003
Posts: 1,374
R
Moderator
Are there any continuos metal paths between the building? Such as water pipe, gas, coax, phone, etc...?


Ryan Jackson,
Salt Lake City
Joined: Apr 2002
Posts: 178
R
Member
Not that I`m aware of at this time.I read 250.32 Not clear on the single branch part.Electricians here say you can run three wire but the best way would be go with 4 wire and the rod.Just would like to better understand if three wire is permisable in this situation legally. But also personally I`m lean towards the best way if it is better.

Joined: Apr 2003
Posts: 139
B
Member
If your installing a panelboard at the workshop, than you don't have a single branch circuit going to the workshop, you have a feeder.

Regardless if you wire with 3-wire or 4-wire, a grounding electrode system will be required at the workshop building.

I don't think either way can be classified as "better". Both will provide adequate service and practical safegaurding.


Bryan P. Holland, ECO.
Secretary - IAEI Florida Chapter
Joined: Apr 2002
Posts: 192
T
Member
Take a course on stray voltage and you will find out why the 4-wire method IS better than using only 3.

If you are not sure of metallic paths then you MUST use 4-wire.

Ground rod(s) are necessary at the second building.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Niko
Niko
Campbell, CA
Posts: 356
Joined: August 2006
Top Posters(30 Days)
NORCAL 5
Trumpy 3
Popular Topics(Views)
300,297 Are you busy
229,978 Re: Forum
214,792 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5