OK ,I have a 200amp service residential.I have a out building/workshop with a 100 amp main breaker panel installed. Now can I run 3 wire service to it?Bond neutral to can. Do I place a rod there or not? Do I run 4 wire and place rod? I re read some past threads but need alittle reassurance.Thanks in advance. using direct burial cable pvc conduit.
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
Are there any continuos metal paths between the building? Such as water pipe, gas, coax, phone, etc...?
Ryan Jackson, Salt Lake City
|
|
|
|
Joined: Apr 2002
Posts: 178
OP
Member
|
Not that I`m aware of at this time.I read 250.32 Not clear on the single branch part.Electricians here say you can run three wire but the best way would be go with 4 wire and the rod.Just would like to better understand if three wire is permisable in this situation legally. But also personally I`m lean towards the best way if it is better.
|
|
|
|
Joined: Apr 2003
Posts: 139
Member
|
If your installing a panelboard at the workshop, than you don't have a single branch circuit going to the workshop, you have a feeder.
Regardless if you wire with 3-wire or 4-wire, a grounding electrode system will be required at the workshop building.
I don't think either way can be classified as "better". Both will provide adequate service and practical safegaurding.
Bryan P. Holland, ECO. Secretary - IAEI Florida Chapter
|
|
|
|
Joined: Apr 2002
Posts: 200
Member
|
Take a course on stray voltage and you will find out why the 4-wire method IS better than using only 3.
If you are not sure of metallic paths then you MUST use 4-wire.
Ground rod(s) are necessary at the second building.
|
|
|