Hospital feeders wiring methods #88077 05/07/04 02:52 PM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline OP
Member
Question

Panel feeders to a general care area not on essential electricial system ,PVC allowed???
I know for branch circuits part b applies approved grounding raceway AND insulated grounding condutor But feeders???
All I can find code references to are Branch circuits.

2017 / 2014 NEC & Related Books and Study Guides
Re: Hospital feeders wiring methods #88078 05/08/04 07:25 AM
Joined: May 2002
Posts: 1,716
R
Roger Offline
Member
Yoopersup, yes PVC is allowed for normal feeders. (Equipment branch also)

Since there are no specific requirements like there are for branch circuits, 517.12 allows using wiring methods from chapters 1 thru 4

Roger

Re: Hospital feeders wiring methods #88079 05/08/04 02:59 PM
Joined: Aug 2001
Posts: 599
N
Nick Offline
Member
517.13(B) says the grounding conductor shall be installed in metal raceways or metal clad cables with the branch circuit conductors. This would imply only back to the panelboard. However,517.13(A) requires a ground path for fault current by a metal raceway system of cable armor assembly.
A ground path for fault current must be continuous to the source of it's supply which in most cases is a transformer and would include the panel feeder.

Re: Hospital feeders wiring methods #88080 05/10/04 08:05 AM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline OP
Member
517.19d Panelboard Grounding Which is a critical area ( I;m talking about is only General care area). Says grounded electrical system is used AND a Metal feeder or raceway OR type mc or mi cables IS installed:::::: So I;m taking it other wiring metods besides metal can be used . This was for Critical and I;m talking about General care. The IS installed again tells me I have other options. Again input is welcomed

Re: Hospital feeders wiring methods #88081 05/10/04 09:52 AM
Joined: May 2002
Posts: 1,716
R
Roger Offline
Member
Yoopersup,
Quote
So I;m taking it other wiring metods besides metal can be used .
this is correct.

517.19 doesn't have any bearing in this application, and even if it did, it would allow "Normal" feeders to be installed as you stated in your sentence above.

Roger

Re: Hospital feeders wiring methods #88082 05/10/04 10:12 PM
Joined: Aug 2001
Posts: 599
N
Nick Offline
Member
I am trying to understand the reason for specifically requiring a redundant path with a metallic raceway from the panel to the devices but falling short of specifically requiring it for the feeder. The way I see it all the electrical redundancy is lost at the panelboard. Like I said above it requires a metallic ground fault path but it appears only from the panel to the device. Not the entire electrical path. [Linked Image]


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
lil suzi
lil suzi
Midwest
Posts: 57
Joined: August 2003
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
270,731 Are you busy
204,964 Re: Forum
193,075 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3