#88063 05/07/04 08:07 PM
Joined: Oct 2001
Posts: 20
W
Member
I would like to back up a second. Why do you have to run a #6 wire? It's a 50 amp circuit, why not run #8 THHN?

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

#88064 05/07/04 09:20 PM
Joined: Oct 2001
Posts: 172
W
Member
Mick
Take a look at 110.14(C)(1)(a) and then go to 310.16. The unit may not be listed and identified for 75C wire.

#88065 05/08/04 12:02 AM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
# 8 is good for 48 amps, and it is a fairly long run anyway.


The Golden Rule - "The man with the gold makes the rule"
#88066 05/09/04 05:34 AM
Joined: Feb 2003
Posts: 197
Z
Member
Most of the Hot Tubs I have wired required # 6 cu conductors,as per manufacturer instructions.
How hot are the attics in your area? You will need to adjust your amps. Also you cannot sleeve NM outdoors, it is still a wet location,even above grade.


Shoot first, apologize later.....maybe
#88067 05/09/04 09:47 PM
Joined: Apr 2002
Posts: 192
T
Member
334.80: NM must be used at the 60* ampacity which is 40A for #8 and 55A for #6. If you run thhn in conduit then the ampacity will be 50A and 65A respectively if the terminations are marked 75*. I'm assuming that no other derating will be necessary.

#88068 05/09/04 10:02 PM
Joined: Jun 2003
Posts: 681
P
Member
If you are running it in the attic (typical here in NY for the summer is about 120 degrees F), that would take a multiplier of .75 times 65 amp (for 6 AWG) which is now rated for 48.75 amps.

Pierre


Pierre Belarge
#88069 05/10/04 12:21 AM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
The attics here in AZ do get hot, probably more than 120 deg. The spa calls for a 50 amp circuit. Derating the #6 might put it close. It would not make sense to do a splice just to run THHN through the pipe in that short run too the disc from the attic.


The Golden Rule - "The man with the gold makes the rule"
#88070 05/10/04 01:05 AM
Joined: May 2004
Posts: 4
J
Junior Member
I agree splices could create possible unwanted problems in the future.Best to not
splice the wire if possible.

(:

Page 2 of 2 1 2

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
The_Lightman
The_Lightman
Orlando, Fl, USA
Posts: 49
Joined: August 2001
Top Posters(30 Days)
Trumpy 6
NORCAL 3
Popular Topics(Views)
300,622 Are you busy
230,304 Re: Forum
215,084 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5