0 members (), 125 guests, and 59 robots.
#87932 05/04/04 06:33 PM
EvanH Offline OP
When wiring industrial 3-phase motors, common practice as I've seen it has been to use wirenuts to connect leads to incoming power wires, and tape them off.
I recently received an IEEE-841 style motor, that has ring terminals on the motor leads. Is there some expectation or regulation that I must use some other kind of wire connection?
Does anyone know a reason I can't just snip off the ring terminals and use the wirenut technique?
Thanks,
Evan
#87933 05/04/04 11:33 PM
Page 19 for MSC-series motor-stub splice. Though there may be local variations, bolted connections in motor j-boxes are fairly universal. http://tnbelectricalworld.tnb.com/contractor/docs/shrinkon.pdf
In some plants, non-bolted splices are a “dismissible” offense. Given IEEE-841 motors are Petroleum and Chemical—Severe Duty, bolted connections are likely a default requirement.
[This message has been edited by Bjarney (edited 05-05-2004).]
#87934 05/05/04 08:42 PM
EvanH Offline OP
Thanks for the response, and the splice insulator reference.
So for the splice itself, I put a similar ring terminal on my power conductor, and just use any bolt and nut that are the right size to fit through the ring terminals?
#87935 05/05/04 10:53 PM
It may be best to use the existing ring terminal to size the machine bolt and ring terminal for external wiring. The T&B MSCs list a maximum bolt length. Zinc-plated steel hardware with star lockwashers have worked well for me.