#87828 04/21/04 11:12 AM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
Is there a limit on the amount of bends when running liquid-tite or other flexible conduit?


The Golden Rule - "The man with the gold makes the rule"
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#87829 04/21/04 11:59 AM
Joined: Sep 2001
Posts: 806
N
Member
No more than 360 degrees total between access points, like any other conduit system.

#87830 04/21/04 06:43 PM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
You would think it might be different because you can run the wire inside before you install the flexible conduit. But if you ever have to pull it out later, could be tuff.


The Golden Rule - "The man with the gold makes the rule"
#87831 04/21/04 06:47 PM
Joined: Jan 2003
Posts: 4,391
I
Moderator
Yeah you can do that, and I am sure we all have done it, but code wise we are not suposed to.

Quote
300.18 Raceway Installations.
(A) Complete Runs.
Raceways, other than busways or exposed raceways having hinged or removable covers, shall be installed complete between outlet, junction, or splicing points prior to the installation of conductors. Where required to facilitate the installation of utilization equipment, the raceway shall be permitted to be initially installed without a terminating connection at the equipment. Prewired raceway assemblies shall be permitted only where specifically permitted in this Code for the applicable wiring method.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#87832 04/28/04 05:26 PM
Joined: Dec 2003
Posts: 18
D
Member
how far are you running the liquid flex if your worried about more than 360 degrees of bends. usually a six foot piece has much less than 360 in bends

#87833 04/28/04 05:42 PM
Joined: Jan 2003
Posts: 4,391
I
Moderator
You can run flex as far as you like. [Linked Image]


Bob Badger
Construction & Maintenance Electrician
Massachusetts