#87654 04/01/04 10:54 PM
Joined: Feb 2004
Posts: 133
E
Member
Can anyone site a code violation for splicing two neutrals together in a junction box, each from a differant branch circuit. Is there a safety issue if this is done?

Horizontal Ad
#87655 04/02/04 01:20 AM
Joined: Jun 2003
Posts: 1,143
D
Member
I think the safety issue is if you have circuit "A" and "B" sharing a neutral, if you disconnect power to "A", and a load is still present on "B", you could get current to ground if you provide a path for it on the joined neutral.

Except on multiwire branch circuits, where all hots are d/c'd by one breaker, I'd stick to the "one hot - one breaker" principle.

And you might weant to check with your AHJ - a lot of municipalities require separate neutrals for each branch circuit.

#87656 04/02/04 04:00 AM
Joined: Aug 2001
Posts: 7,520
P
Member
The wording in 310.4 seems to imply that only conductors size 1/0 and larger may be paralleled, although it doesn't actually say so directly.

#87657 04/02/04 04:40 AM
Joined: Mar 2004
Posts: 391
B
Member
Considering that 310.4, "Exception No. 2" specifically deals with applications where conducters smaller than 1/0 are allowed to be paralleled, I think it's safe to say that 310.4 applies exclusively to 1/0 and larger unless otherwise noted.

ElectricIan
Why do you want to splice the neutrals from independent branch circuits to begin with?
[Linked Image]

-John

#87658 04/02/04 04:58 AM
Joined: Jan 2003
Posts: 4,391
I
Moderator
As has been stated 310.4 along with the conductors being smaller than allowed for paralleling, they would also have to meet all the requirements of 310.4

Quote
The paralleled conductors in each phase, neutral, or grounded circuit conductor shall
(1) Be the same length
(2) Have the same conductor material
(3) Be the same size in circular mil area
(4) Have the same insulation type
(5) Be terminated in the same manner
Where run in separate raceways or cables, the raceways or cables shall have the same physical characteristics. Conductors of one phase, neutral, or grounded circuit conductor shall not be required to have the same physical characteristics as those of another phase, neutral, or grounded circuit conductor to achieve balance.

Parallel conductors have to have the same characteristics as each other so each gets an equal share of the load.

If you have tied the neutrals from two or more branch circuits together you have the potential for the neutrals to have to carry two or more times the current rating of one branch circuit.

Example.

You have tied together the neutrals of two 14/2 NM, 15 amp branch circuits on the same phase together.

One of these cables takes a direct route to the panel, the other cable goes all over the house before getting back to the panel.

Now load both of the hots of these circuits to 15 amps and the two paralleled neutrals have to deal with 30 amps.

Because of the different lengths the current will not split equally and you may have 20 amps on the short 14 AWG and only 10 amps on the longer 14 AWG.

There is also 300.3(B) Conductors of the Same Circuit.

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#87659 04/02/04 07:44 AM
Joined: Feb 2004
Posts: 133
E
Member
I don't want to do splice the neutrals together. I agree with all that this is in general a bad thing to do. I just counldn't find it in the code book and am just asking if anyone has come across a ruling against it specifically stated in the code book.

#87660 04/02/04 09:13 PM
Joined: Feb 2004
Posts: 133
E
Member
Thanks to all for the feedback on this question, especially Bob for such an excellent and thorough explanation along with the code reference.

Horizontal Ad

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
RonKipperDatacom
RonKipperDatacom
Kansas City, KS
Posts: 30
Joined: January 2013
Top Posters(30 Days)
Popular Topics(Views)
333,172 Are you busy
258,340 Re: Forum
239,914 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5