#87534 03/16/04 07:46 PM
Joined: Mar 2003
Posts: 92
G
gserve Offline OP
Member
Is there a code prohibiting a cord and plug supplying the power to a all in one emergency light?

2017 / 2014 NEC & Related Books and Study Guides
#87535 03/16/04 09:17 PM
Joined: Aug 2003
Posts: 1,374
R
Moderator
No, unless there is a local one that I am not aware of.


Ryan Jackson,
Salt Lake City
#87536 03/17/04 10:57 AM
Joined: Dec 2003
Posts: 751
E
Member
700.12(E) Unit Equipment specifically allows it:
Quote
Flexible cord-and-plug connection shall be permitted, provided that the cord does not exceed 900 mm (3 ft) in length. The branch circuit feeding the unit equipment shall be the same branch circuit as that serving the normal lighting in the area and connected ahead of any local switches.


Earl

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Top Posters(30 Days)
Admin 10
Popular Topics(Views)
280,476 Are you busy
213,562 Re: Forum
200,434 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5