#87499 03/13/04 11:26 PM
Joined: Jan 2004
Posts: 1,507
G
Member
I've always enforced the need for a properly sized J-box for splicing fixture wires to the branch circuit conductors and not permitted the installer to rely on the canopy for this purpose. Am I wrong?


George Little
2017 / 2014 NEC & Related Books and Study Guides
#87500 03/14/04 09:44 AM
Joined: Dec 2000
Posts: 4,287
Member
Up to 4 #14 or smaller fixture wires aren't counted in box fill anyway, so a box that is properly sized for the branch circuit conductors is sufficient. See 314.16 (B)(1) Exception.

410.10 Space for Conductors
Canopies and oulet boxes taken together shall provide adequate space so that luminaire (fixture) conductors and their connecting devices can be properly installed.
The italics are mine.

#87501 03/14/04 04:15 PM
Joined: Jan 2004
Posts: 1,507
G
Member
Thanks for your insight. I guess I'll will take a different view of this subject thanks for the code reference. I still am kinda nervous about allowing someone to install a 3" pan box with two 14/2 w/g for connection of a luminaire. I think I'll ask him for some specs on the proposed fixture, I'm sorry, luminaire.


George Little
#87502 03/14/04 05:27 PM
Joined: Apr 2002
Posts: 558
C
Member
George

The exception that Scott (electure) posted above applies to the fixture wires not the branch circuit conductors. Using a 3/0 pancake box with even one 14-2 NM cable is a violation unless the box is extended with an extension ring or canopy that is marked with its cubic inch capacity. I have never seen a fixture canopy that has been marked with its capacity. A single 14-2 NM cable would require a minimum of 6 cubic inches if an external clamp is used or 8 cubic inches if an internal clamp is used. A 3/0 pancake has a 4 cubic inch capacity. Two 14-2 NM cables would require 10 cubic inches with internal clamps or 12 cubic inches with internal clamps.

Curt


Curt Swartz
#87503 03/14/04 11:17 PM
Joined: Aug 2003
Posts: 1,374
R
Moderator
When I inspect I allow (1) 14-2 NM cable in a 3-0 pancake box. I realize that it is not permitted, but I also realize that sometimes that is the only way you can go about the installation. I will not, however, allow (2) 14-2's or (1) 12-2.


Ryan Jackson,
Salt Lake City
#87504 03/23/04 10:01 PM
Joined: Apr 2002
Posts: 189
T
Member
Actually, electure, those four fixture wires you refer to have to be SMALLER than #14 (not "14 or smaller") in order to avoid using them in fill calculations. See: 314.16(B)(1)

#87505 03/24/04 07:33 PM
Joined: Aug 2001
Posts: 459
J
Member
Ryan,

Why don't they use 4" pancake boxes instead of the 3". I have only seen the 3" on very old work like K&T. Is this a regional thing?

#87506 03/24/04 08:37 PM
Joined: Aug 2003
Posts: 1,374
R
Moderator
Hi Jim. I wish I could answer your question, but I'm afraid that it is a question I also ask. I can't figure it out. :0


Ryan Jackson,
Salt Lake City
#87507 03/27/04 12:56 AM
Joined: Jun 2003
Posts: 681
P
Member
If the installation of a 4 inch canopy on a 3 inch box is performed where the surface is combustible, it is a violation of 410.13.

Pierre


Pierre Belarge
#87508 03/27/04 12:53 PM
Joined: Dec 2000
Posts: 4,287
Member
Triple,
Thank You! Sometimes I suffer from "Hoof in Mouth" disease.

Smaller than #14...S


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Samurai
Samurai
Fl.
Posts: 46
Joined: May 2007
Top Posters(30 Days)
timmp 8
Rachel 4
djk 2
Popular Topics(Views)
281,588 Are you busy
215,225 Re: Forum
202,069 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5