Does the code require an "in-use cover" on an outside receptacle, that is on a porch area, and has a roof over it?? Thanks Steve..
|
|
|
|
Joined: Feb 2004
Posts: 33
Member
|
would that only be considered a "damp location"?
|
|
|
|
Joined: Oct 2002
Posts: 830
OP
Member
|
jeff, yes I think that would only be considered a damp location. Do you know the code reference for the in use requirements? Thanks Steve...
|
|
|
|
Joined: Nov 2003
Posts: 269
Member
|
406.8(B)contains the requirements for using "in-use" covers in wet locations.
John
|
|
|
|
Joined: Aug 2003
Posts: 64
Member
|
Am I the only one that sees this expanded requirement for "in use" covers as a poor requirement? I have felt that within a few monthes many of these "in use" covers will become "no covers" due to the flimsey construction and I know of at least one case where my prediction has come true.
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
EPrice: I agree with you, but unfortanatly, the NFPA doesn't agree with us I require them.