ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Photos of the Week:

Nightmare Panels
Nightmare Panels

Random Gallery Image:
Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 379 guests, and 16 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 2 1 2
#87138 01/25/04 03:34 PM
Joined: Nov 2002
Posts: 267
W
Member
What are some of the requirements for installing a sub-panel in a detached garage as far as grounding is concerned? Is it just a 4-wire isolated netral at the sub panel? What about an additional ground rod? Have any of you done these installations and how did it go with the inspector?

~Andy

Horizontal Ad
#87139 01/25/04 07:07 PM
Joined: Jun 2002
Posts: 186
M
mj Offline
Member
if only one branch circuit is connected to the building, no ground rod is required.

#87140 01/25/04 07:46 PM
Joined: Jan 2003
Posts: 4,391
I
Moderator
Two code options for running a feeder to a separate structure, both require ground rods and any other electrodes present to be used.

1)3 wire feeder with neutral bonded to ground at the added panel.

This method is only allowed if there are no continuous metallic paths bonded to the grounding system in both buildings or structures involved.

In other words no parallel paths for neutral current.

2)4 wire feed with isolated neutral bar and bonded grounding bar.

Look at 250.32(B)(1) and (2)


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#87141 01/28/04 06:08 PM
Joined: Oct 2000
Posts: 5,393
S
Member
the 3 wire/4 wire argument goes round in circles with those opposed to 3 wire pointing to even acidic soil, and those that advocate it pointing to standard poco installs

the 'one circuit' exception forgoing the G-rod ends up inevitably w/3 ph multiwire circuits, or an OCPD as definitoinal benchmarks.

#87142 01/28/04 09:35 PM
Joined: Feb 2003
Posts: 169
R
Member
Bob:

Is it your contention that this is a "feeder" going out to the garage, and not a branch circuit(multiwire), because it is fed from a circuit breaker that is not the final overcurrent device.
The final overcurrent device being the branch circuit breakers in the panel that's in the garage.

Branch Circuit. The circuit conductors between the final overcurrent device protecting the circuit and the outlets.

Russ

[This message has been edited by russ m (edited 01-28-2004).]

#87143 01/28/04 09:50 PM
Joined: Aug 2003
Posts: 1,374
R
Moderator
Russ: The original post asked about installing a panel at a detatched structure. This would require that a FEEDER circuit be installed, since the panel contains OCPD's, not outlets.


Ryan Jackson,
Salt Lake City
#87144 01/28/04 10:08 PM
Joined: Feb 2003
Posts: 169
R
Member
Thanks Ryan

I was just try to word it so we all understood it, I was a bit confused at first.

Horizontal Ad
#87145 01/29/04 05:41 PM
Joined: Jan 2003
Posts: 4,391
I
Moderator
Thanks for the assist Ryan and yes that was what I was going for.

A single branch circuit including a multiwire branch circuit you could forget about the ground rod, I know I would. [Linked Image]

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#87146 01/29/04 05:43 PM
Joined: Jan 2003
Posts: 4,391
I
Moderator
Oh and if someone could explain the reason one circuit does not need a ground rod and two circuits require a ground rod I would really like to know.

Sparky, what have you heard for this? [Linked Image]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#87147 01/29/04 07:00 PM
Joined: Oct 2000
Posts: 5,393
S
Member
Quote
Sparky, what have you heard for this?

usually the converstaion turns to the technicalities of making a G-rod GEC onto a single pole switch...

at which point conceeding to the branch circuit exception seems reasonable

~S~

Page 1 of 2 1 2

Link Copied to Clipboard
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5