ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Photo of the Week:

Creative Service Support
 "Creative" Service Support

Advertisement:-Left
Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
1 members (Scott35), 152 guests, and 29 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: May 2002
Posts: 1,716
R
Roger Offline OP
Member
Opinions with code references please.

Optional Standby Generator with 600 amp breaker in onboard enclosure, Service Rated and Listed by special order.

Generator is SDS and sits 50' from entrance into mech room where another switch is installed adjacent to Normal power MDP.

Does anybody know of a reason per any codes that there should be a Service Rated Switch installed closer to the building, or that the interior switch should be located nearest point of entrance per 230.70(A)(1).

Also with this Service Disconnect located at the Generator, wouldn't we be meeting 230.72(B)?

Roger

Horizontal Ad
Joined: Feb 2003
Posts: 169
R
Member
I'm stumped!
Can't help at all.
Doesn't the feeder usually go directly from main switch in the generator to the tansfer switch?

Joined: Nov 2000
Posts: 2,148
R
Member
Roger,
Is the generator in the same building as the MDP?
Don


Don(resqcapt19)
Joined: May 2002
Posts: 1,716
R
Roger Offline OP
Member
Hello Russ and Don.

Don the generator sits outside the building and is feeding a UPS in a computer room. (this is at a university and backs up the network campus wide)

The state inspector, who I've not spoke with yet, left the job with out inspecting the installation saying or implying the generator disconnect (enclosed breaker) could not be used for the service disconnect even though it is listed as such.

Roger

Joined: Nov 2000
Posts: 2,148
R
Member
Roger,
If the generator is at a second building then wouldn't 225.31 require a disconnect at the main building located per 225.32? Or does this installation meet Exception #1 to 225.32?
Don


Don(resqcapt19)
Joined: Jun 2003
Posts: 681
P
Member
The generator is not a service as per the 2002 NEC.
Service (Article 100). The conductors and equipment for delivering electric energy from the serving utility to the wiring system of the premises served.

This installation falls under 225.30(A)(4)

I believe as Don has stated that the exception #1 to 225.32 would make the described installation compliant with the NEC. The switch still has to follow 225.36 Suitable for Service Equipment.

Pierre


Pierre Belarge
Joined: Mar 2001
Posts: 345
T
Member
For most AHJs the conditions of maintenance and supervision that would fulfill the exception is full time on site electrical staff.
--
Tom H


Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison
Horizontal Ad

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
pcsailor
pcsailor
Minneapolis, MN, USA
Posts: 21
Joined: September 2019
Top Posters(30 Days)
BigB 4
Jam85 4
Popular Topics(Views)
327,993 Are you busy
252,847 Re: Forum
235,481 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5