0 members (), 331 guests, and 10 robots.
Question:
When performing an insulation test using a megger on cables in a 600 volt system, megger scale is 1000 volt dc.
Why do cable manufacturer's recommend a megger scale of 500 volt dc?
Ron Offline
According to NETA:
7.3.2 Cables, Low-Voltage, 600 Volt Maximum
Perform insulation-resistance test on each conductor with respect to ground and adjacent conductors. Applied potential shall be 500 volts dc for 300 volt rated cable and 1000 volts dc for 600 volt rated cable. Test duration shall be one minute.
Ron
Ron, what does NETA stand for? Do they have a web site?
Rick
I hope you will forgive a wild % guess. Below is the URL of the InterNational Electrical Testing Association.
http://www.netaworld.org/
Tom Horne
Tom Horne