Report on Comments - May 2004
196 Log #385 NEC-P05
(250. 119)
Submitter: Dan Leaf Rancho Santa Margarita, CA
Comment on Proposal Number: 220
Recommendation:

Revise last sentence: Conductors with insulation or individual covering that is green , green with one or more yellow stripes , or otherwise identified as permitted by this section shall be used only as an equipment bonding conductor.

Exception: Grounding electrode conductors shall be permitted to be identified in accordance with this section.

Substantiation:

Since this section encompasses individual covered conductors, they should be covered by the proposal. Many installers employ green covering, marking, or striping for grounding electrode conductors , though not required or prohibited by present Code, which provides a degree of identification from circuit conductors, especially where installed with other conductors in the same raceway or enclosure. Though this section relates to equipment grounding (bonding) conductors the wording appears applicable as a general rule.

Final Action:

CMP 5 Accepted this "Comment in Principle" and added the following to the existing 250.119 in the NEC.

"Conductors with insulation or individual covering that is green, green with one or more yellow stripes, or otherwise identified as permitted by this section shall not be used for grounded or ungrounded circuit conductors"



[This message has been edited by Joe Tedesco (edited 12-04-2003).]


Joe Tedesco, NEC Consultant
Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

Joined: Oct 2000
Posts: 5,392
S
Member
the sqeaky wheel method seems very effective in the nfpa...

Joined: Aug 2001
Posts: 7,520
P
Member
While specifying that green (or green/yellow) be used for grounding conductors, it seems only logical to me that these colors should also be prohibited from use for other functions.

Joined: Oct 2000
Posts: 4,081
Likes: 3
Member
Quote
"Conductors with insulation or individual covering that is green, green with one or more yellow stripes, or otherwise identified as permitted by this section shall not be used for grounded or ungrounded circuit conductors"
It only makes sense to close a loophole when one is found.

[Linked Image]
Bill


Bill

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
watersparkfalls
watersparkfalls
Washington...Not DC
Posts: 240
Joined: March 2005
Top Posters(30 Days)
BigB 9
Popular Topics(Views)
302,454 Are you busy
231,865 Re: Forum
216,401 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5