Grounding electrode conductor #86596 11/14/03 01:23 PM
Joined: Feb 2001
Posts: 89
E
electrician02125 Offline OP
Member
Good afternoon

I am wiring a residential building with 4 units. Each of the units will have their own water supply and meter. I have installed the typical 5 gang meter pack (4 plus public)with service disconnects directly next to the meters.

For grounding I have ran a continuous number 2 copper conductor the length of the building and split bolt connected short lengths down to each water line to bond all back to the main service equipment ground lug. I have also driven a supplemental ground rod at the meter enclosure and ran number 4 to the rod as a supplemantal ground.

The Inspector loved it but I would like your opinion.

2017 / 2014 NEC & Related Books and Study Guides
Re: Grounding electrode conductor #86597 11/14/03 11:16 PM
Joined: Dec 2002
Posts: 308
E
Edward Offline
Member
I thought the code did not allow reversable connections on the grounding system or the GEC or the water pipe bond.

Edward


Thanks
Edward
Re: Grounding electrode conductor #86598 11/15/03 08:10 AM
Joined: Jan 2002
Posts: 1,457
E
Electricmanscott Offline
Member
If you ran the gec continuous to one electrode then tapped off using split bolts to each unit water service you are not splicing the electrode. The taps are really bonding jumpers to each addtional water service. You should have two supplemental rods unless you have 25 ohms or less on one. You only need # 6 to the rods.

Re: Grounding electrode conductor #86599 11/15/03 08:21 AM
Joined: Apr 2003
Posts: 13
B
Branch Offline
Member
You might want to look at Art: 250.64(C)this will explain the type of splice connectors allowed for grounding. (Irreversible compression-type connector) (Exothermic welding process)

Re: Grounding electrode conductor #86600 11/15/03 09:03 AM
Joined: Apr 2003
Posts: 13
B
Branch Offline
Member
I think if you have water service in each unit that will be a main ground you have to run seperate grounds from each water line back to your service equipment.

Re: Grounding electrode conductor #86601 11/15/03 09:40 PM
Joined: Jul 2001
Posts: 37
R
RickG Offline
Member
From what I gathered from the info provided, the water pipes in each unit are bonded, they are not ground electrodes. I am assuming that the underground portion of the water services is plastic, if not the following does not apply. The code requires a continuous conductor to the main ground electrode, in this case the ground rods. The H2O bond wire is allowed to be tapped/spliced as long as it is sized to the service entrance conductors, not the breaker size. I don't know what size SE conductors were run, but fromwhat I see this is a code compliant installation.
Now after rereading the original post, if the water underground services are indeed metalic... you would have to go to the main ground electrode unspliced. Could any ONE of the water services be the main ground electrode and the other 3 be supplental?
I think that is how I would look at it in my town.
If this is the case as long as you go to any one of the water services unspliced (even the last one) you could splice to the other 3.

Re: Grounding electrode conductor #86602 11/16/03 07:17 AM
Joined: Feb 2003
Posts: 169
R
russ m Offline
Member
If the water service is metal underground it sounds code compliant to me.

Re: Grounding electrode conductor #86603 11/16/03 08:28 AM
Joined: Apr 2003
Posts: 13
B
Branch Offline
Member
If the main water services are plastic entering the building i think you can run your bond back to each sub-panel in each unit or you can splice the bonds and run back to service equipment or to ground rod or rods. Any thoughts on this would be a help to understanding this.

Re: Grounding electrode conductor #86604 11/16/03 09:40 AM
Joined: Feb 2001
Posts: 89
E
electrician02125 Offline OP
Member
Thank you all for the input.

The 3 water services are all copper throughout. I do in fact have a continuous connection from the furthest water service back to the main GEC lug. The remaining two water services I have simply exposed some of the copper on the continuous GEC and split bolted them that way. Sort of like a continuous ground bus running the length of the building. On one end I have the conductor landed on the main GEC lug and the other is on the furthest water line....continuous with no breaks in the conductor. I hope this makes sense.

Re: Grounding electrode conductor #86605 11/16/03 08:41 PM
Joined: Jul 2001
Posts: 37
R
RickG Offline
Member
02125
Sounds like a fine, code compliant installation to me.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
cookcc
cookcc
California ,Long Beach
Posts: 28
Joined: May 2007
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Admin 1
Popular Topics(Views)
270,702 Are you busy
204,943 Re: Forum
193,053 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3