ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Violation?
by renosteinke - 01/27/23 09:52 PM
Does NEC 551.71 (F) apply to dwellings?
by BigB - 01/20/23 10:46 AM
Power submeter connections
by HotLine1 - 01/19/23 09:09 AM
AFDD's coming to the UK
by Texas_Ranger - 01/17/23 07:22 PM
New in the Gallery:
Burger King crown sillyness
Burger King crown sillyness
by wa2ise, December 11
240/208 to a house
240/208 to a house
by wa2ise, October 9
Who's Online Now
0 members (), 17 guests, and 17 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#86578 11/12/03 07:58 PM
Joined: Sep 2003
Posts: 114
B
Member
A home owner called me out to resolve a dispute he is having with a home warranty company over his spa. The spa is leaking and the company subed out to fix it won't touch it because it is wired to the disconnect with Alumunum wire. It is a 50 Amp 240 Volt sub-panel with a GFCI breaker. The wire size looks to be #8 which I believe is too small. But that isn't the issue the company is raising. They are saying the alumunum ground wire is not to code. I might add that from the sub-panel to the spa itself, it is wired with #8 copper and #10 copper for ground. All connections in sub-panel use anti-oxident. Does anyone have any insight into this, or can point me to the right place in the NEC where I can find the answer?

Many thanks,
Byron Wise

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

#86579 11/12/03 08:37 PM
Joined: Aug 2003
Posts: 173
S
Member
Many spa instructions specifically say to use #6cu, even though this is overkill for 50 amps. #8 al is undersized for 50 amps but this should have no bearing on the spa. The manufacturer has no say in what you feed a panel with and is looking for a scapegoat. The fact that they think something is not to code is no reason to void a warranty due to a leak. If it were an electrical problem I can see them causing a stink.
I can't refrence the exact article but it's right in 680. Within the structure conventional wiring methods can be used. Romex and aluminum wire included. Once you exit the structure the pool/spa codes become stringent.

We run 8/3 for spa feeds unless #6 is specified. Then 4-#8's (or #6's) in sealtite to the spa itself from the disconnect.


Speedy Petey

"Anyone who has never made a mistake has never tried anything new." -Albert Einstein

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mxslick
mxslick
Atomic City, ID USA
Posts: 806
Joined: October 2004
Top Posters(30 Days)
BigB 9
triple 3
Popular Topics(Views)
302,561 Are you busy
231,910 Re: Forum
216,545 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5