#86516 11/06/03 10:49 PM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
Not sure if its legal to mount an outdoor ceiling fan in a ramada with a lattice type ceiling in which rain will come through. The fan motor looks sealed but I may have figure a way to seal the cover above where the connections are. Don't believe this is addressed in the code?


The Golden Rule - "The man with the gold makes the rule"
2017 / 2014 NEC & Related Books and Study Guides
Joined: Jun 2001
Posts: 642
N
Member
If the cieling fan is rated for a wet location, I do not see a problem.
I personally have yet to see a wet location cieling fan. I have installed industrial type of fans in wet locations, but they were not designed for looks.
I would check the manufacturers installation instruction very carefully.


ed
Joined: Aug 2003
Posts: 1,374
R
Moderator
I've seen some wet location fans. Next time your at Lowe's or Home Depot take a look, they usually have 2 or 3 on display.

I've never hung one, but after looking at them from a distance I think they could be mounted in that situation.

That being said, I think NEsparky hit it on the head though: check the manufacturer's specs very carefuly


Ryan Jackson,
Salt Lake City
Joined: Apr 2002
Posts: 2,527
B
Moderator
From 2003 UL White Book: FANS, CEILING-SUSPENDED (GPRT)

Fans intended for mounting beneath a ceiling structure such as provided on porches or patios have been subjected to a rain test and are marked as being acceptable for such use…

Fans evaluated for use in barns, poultry houses, dairy barns or the like, as covered by Article 547 of the National Electrical Code, are marked ‘‘For Use in Agricultural Buildings’’ or with an equivalent statement…





[This message has been edited by Bjarney (edited 11-07-2003).]


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
The Watt Doctor
The Watt Doctor
Mont Belvieu, TX
Posts: 437
Joined: December 2001
Top Posters(30 Days)
Trumpy 10
Admin 10
Popular Topics(Views)
280,448 Are you busy
213,527 Re: Forum
200,406 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5