#86508 11/06/03 11:38 AM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
If a 50a 240v outdoor spa has the GFI on the plug, can I run the circuit not using a GFI breaker?


The Golden Rule - "The man with the gold makes the rule"
2017 / 2014 NEC & Related Books and Study Guides
#86509 11/06/03 01:07 PM
Joined: Dec 2002
Posts: 308
E
Member
I believe if you feed a gfci device with another gfci device it will nuisance trip.
The gfci plug or disconnect should suffice which will be fed by a 50 amp dp breaker.

Edward


Thanks
Edward
#86510 11/06/03 02:13 PM
Joined: Oct 2000
Posts: 4,035
Likes: 1
Member
Edward,

If the Tub has a Cord and Plug the receptacle itself must be GFCI protected. It makes no difference if there is a GFI on the plug or not.

See:

680.42(A)(2) for outdoor locations.
680.43(A)(3) for indoor locations.

Bill


Bill
#86511 11/06/03 04:12 PM
Joined: Dec 2001
Posts: 35
B
Member
I am not aware of a 50 Amp, 240 volt GFCI Plug - The spa should be protected by a circuit breaker - also, having a GFCI breaker feed a GFCI receptacle will not cause tripping of either device. Only ground currents will trip them.

#86512 11/06/03 08:00 PM
Joined: Nov 2002
Posts: 267
W
Member
I perfer the spa disco. 50 or 60 amp models mostly. 240 volt. self contained 3R enclosure. comes with a dead front GFI which is attached to the coil of a contactor. Feed it from a regular circuit breaker.

#86513 11/08/03 03:48 AM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
This spa does have a built in GFI in the control box. I suppose I wouldn't need a GFI breaker then? And since the panel is within sight, I wouldn't need a disconnect at the spa either.


The Golden Rule - "The man with the gold makes the rule"
#86514 11/08/03 11:26 AM
Joined: Oct 2000
Posts: 4,035
Likes: 1
Member
Al,

You said it has a plug. If there is an outlet for this Tub the outlet itself has to be GFCI protected, it doesn't matter what is in the Tub or on the plug.

See:

680.42(A)(2) for outdoor locations.
680.43(A)(3) for indoor locations.

Bill


Bill
#86515 11/08/03 11:48 AM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
Bill, no it doesn't have the plug, I wired it direct, but there is a GFI built into the spa control panel. Think I will put a GFI breaker in too. That will protect the line going out to it.


The Golden Rule - "The man with the gold makes the rule"

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
SafetyWired
SafetyWired
Pa, USA
Posts: 44
Joined: July 2013
Top Posters(30 Days)
Trumpy 10
Admin 10
Popular Topics(Views)
280,437 Are you busy
213,510 Re: Forum
200,399 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5