#86334 10/14/03 08:57 AM
Joined: Oct 2003
Posts: 2
R
rusty1 Offline OP
Junior Member
Need a little help in confirming my interpretation of 427 and specifically 427.22 from 2002 code. It appears that only electric heating systems that utilize heat trace or flexible heating panels require ground fault protection? Is this because they have no grounded external sheath as in earlier editions of the code?

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

#86335 10/14/03 10:32 AM
Joined: Nov 2000
Posts: 2,148
R
Member
Rusty,
The heat tape and heating panels must have a grounded conductive coating. Note that in previous codes, this covering was required to be metallic, but in the 2002 code it was changed to permit nonmetallic conductive coatins to be used. See 427.23. GFP was required even when the heat trace had a grounded metallic covering. The GFP is required because resistance heating can fail in a manner that will produce enough heat to start a fire without pulling enough current to open the overcurrent protective device.
Don


Don(resqcapt19)
#86336 10/14/03 11:07 AM
Joined: Oct 2003
Posts: 2
R
rusty1 Offline OP
Junior Member
Thanks a lot Don,
I guess I just wondered what makes the heat tape different say from a hot water heater or the numerous other resistance heater apps that do not require GF protection.

#86337 10/14/03 12:39 PM
Joined: Nov 2000
Posts: 2,148
R
Member
Rusty,
I think that there is a lot more potential for damage to heat tracing than other types of resistance heating.
Don


Don(resqcapt19)
#86338 10/17/03 06:15 AM
Joined: Mar 2001
Posts: 2,056
R
Member
I'll second Don on the damage issue.
When installed under pipe insulation, in order to help minimize potential damage, the outer sheath of the insulation should even have warning stickers(supplied from the manufacturer)to indicate that electric heat tracing is installed underneath.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
dougwells
dougwells
kamloops BC Canada
Posts: 1,158
Joined: May 2003
Top Posters(30 Days)
BigB 9
triple 3
Popular Topics(Views)
302,553 Are you busy
231,906 Re: Forum
216,541 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5