#86331 10/08/03 06:39 PM
Joined: Aug 2001
Posts: 7,520
P
pauluk Offline OP
Member
I'm looking at the current requirements for the service connection to a mobile home.

Per the 2002 NEC, 550.16, and part (A)(1) specifically, clearly requires that neutral and ground must be kept separate on the mobile home and prohibits the grounding of appliance frames to the neutral. 550.10(B) specifies a 4-wire supply cord.

550.16(C)(1) requires that the chassis be bonded to the grounding bus in the panel.

Question:
I was browsing another site and read an item which suggests that in the past it was allowable for a mobile home to be fed via a 3-wire connection with N-Gnd bond at the panel.

Is this true?

How about the requirement of 550.16(C)(1) to bond the chassis -- Has this always been the case?

P.S. I'm ignoring the exception which allows N-Gnd bonds if the service equipment is attached to a "manufactured home" in accordance with 550.32(B), and just assuming that the service is located on a nearby post.


[This message has been edited by pauluk (edited 10-08-2003).]

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#86332 10/08/03 09:02 PM
Joined: Apr 2002
Posts: 2,527
B
Moderator
I don't think the N-Gnd bond at the panel has been allowed at keast since the early 1970s.

#86333 10/11/03 06:02 PM
Joined: Aug 2001
Posts: 7,520
P
pauluk Offline OP
Member
So 30+ years of 4-wire supplies? Thanks.

Grounding and bonding issues seem to be an area where ideology changes over the years, both in the U.S.A. and the U.K.