Joined: Feb 2003
Posts: 3
K
KenO Offline OP
Junior Member
Can anyone enlighten me in what article it address's the violation of using a different manufactueur' breaker in someone elses pnl/loadcenter.

Ie... using a ITE breaker in a Crouse hinds load center

Thanks

Ken

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Aug 2003
Posts: 1,374
R
Moderator
110.3(B). (the hardest article in the world to enforce!) I have e-maile a couple different manufacturers and they have replied that their products are not listed for use with other panels/breakers. I do believe that are a very few breakers that are listed for use in other panels, but are the panels listed to recieve them? I doubt it.


Ryan Jackson,
Salt Lake City
Joined: Sep 2002
Posts: 943
Likes: 2
N
Member
I-T-E is owned by Seimens and they bought the Crouse-Hinds/Murrey line, you should be able to get a letter from them on approved
replacements.

Joined: Nov 2000
Posts: 2,148
R
Member
While the panel manufacturers will tell you that you can only use thier listed breakers in the panel, that is not correct and is one of the reasons that 110.3(B) only applies to instructions that are part of the listing and labeling. 110.3(B) does not require compliance with manufacturers instructions. There are UL "classified" breakers that are permitted to be used in panels made by other companies. The use of these "classified" breakers is code compliant and does not void the panel listing.
See UL Guide DIXF. "This category(DIXF) covers Classified molded-case circuit breakers rated 15 to 50 A, 120/240 V maximum that have been investigated and found suitable for use in place of other Listed circuit breakers in specific Listed panelboards." Note that classified breakers are required to be supplied with a list of panels that they can be used in.
Don



[This message has been edited by resqcapt19 (edited 09-05-2003).]


Don(resqcapt19)
Joined: Feb 2001
Posts: 308
S
Member
Does a manufacturer have to honor a warranty if you don't follow their instructions as long as the product is used as listed?

I know this issue is not enforceable, but it is something additional to think about. Then again I've never seen anyone return a panel because of a manufacturer defect.

Joined: Nov 2000
Posts: 2,148
R
Member
Steve,
I did some reserch on the warranty issue a few months ago. It appears that if a contractor installs the "classified" breaker that the panel manufacturer could void the warranty, but if the building owner or end user installs the classified breaker, the warranty stands.
Don


Don(resqcapt19)