Working space around transformers #85635
07/25/03 01:00 PM
07/25/03 01:00 PM
S
steve66  Offline OP
Member
Joined: Mar 2003
Posts: 25
Does the working space in Article 110.26 apply to transformers? Would a 480V panelboard across the isle from a 480 to 208 transformer require 4' between them? Also, do the working space requirements apply to the sides of the transformer? If not, how much space would required on the sides to run conduit in and pull wire (aren't transformers usually fed with a LB into to side?) I am laying out an electrical room, but I'm not an electrician, and I'm not sure how the connections to transformers are usually made.

Finally, can the transformer be backed right up aginst a wall, or does it need breathing room behind it?

2017 / 2014 NEC & Related Books and Study Guides
Re: Working space around transformers #85636
07/25/03 02:13 PM
07/25/03 02:13 PM
B
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
99NEC 450-9. Transformers with ventilating openings shall be installed so that the ventilating openings are not blocked by walls or other obstructions. The required clearances shall be clearly marked on the transformer.

110-16 working clearances would not be modified by ventilation clearances.

Re: Working space around transformers #85637
07/25/03 10:17 PM
07/25/03 10:17 PM
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Quote
450.13 Accessibility.

All transformers and transformer vaults shall be readily accessible to qualified personnel for inspection and maintenance ...


Joe Tedesco, NEC Consultant
Re: Working space around transformers #85638
07/26/03 06:33 AM
07/26/03 06:33 AM
R
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
Working clearances are required to perform preventative maintenance on the xfmr. Granted that most PM can be done with the xfmr not energized, but some will be done live (such as infrared measurements). You will need at least condition 2, possibly condition 3 depending on the interpretation of the AHJ.

[This message has been edited by Ron (edited 07-26-2003).]


Ron

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HotLine1
HotLine1
Brick, NJ USA
Posts: 6,917
Joined: April 2002
Show All Member Profiles 
Top Posters(30 Days)
sparky 20
Admin 20
Potseal 13
Popular Topics(Views)
243,537 Are you busy
180,340 Re: Forum
170,829 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.014s Queries: 14 (0.003s) Memory: 0.9594 MB (Peak: 1.0906 MB) Zlib enabled. Server Time: 2018-01-18 14:10:21 UTC