ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 200 guests, and 12 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#85590 07/18/03 04:50 PM
Joined: Mar 2001
Posts: 2,056
R
Redsy Offline OP
Member
A 600 240 volt 3phase service disconnect feeds a wireway that supplies several feeder disconnects.
One of the feeders supplies a wireway, with the conduit acting as EGC.
The wireway supplies 4 disconnects that feed 4 breaker panels via SER cable.
In each disconnect, the grounding conductor and neutral from the SER are connected together to the neutral lug, which is floating (not bonded).
All passed inspection.
What am I missing?

Work Gear for Electricians and the Trades

Workgear for Electricians

#85591 07/19/03 08:10 AM
Joined: Jun 2003
Posts: 681
P
Member
Redsy
You did not miss a thing, the inspector and the contractor both missed something.
I am a Grounding and Bonding nut,and one of my friends loves to say "grounding and bonding are overrated". We both get a good laugh, seems the contractor and the AHJ also got a good laugh.

Pierre


Pierre Belarge
#85592 07/19/03 08:25 AM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
Take a look at 250.142 A & B. Also, 310.4, which will go away when you correct the connection between the grounding conductor & the grounded conductor.

Also, how are the disconnects grounded? If they are fed by SER cable, the needs to be a connection to the grounding conductor.


Few things are harder to put up with than the annoyance of a good example.
#85593 07/20/03 09:46 AM
Joined: Mar 2001
Posts: 2,056
R
Redsy Offline OP
Member
Thanks,Guys.
Tom,
The disconnects are grounded via grounding locknuts. The voltage is 240, and no remaining KO rings exist, so that is sufficient. A grounding lug would have done the job correctly.
The thing that puzzles me is that, if the neutral & ground are isolated in the panelboards (I haven't looked yet), and the Neutral/Ground connection is floating in the disconnect enclosure, where is the parallel path for neutral current.
I will try to draw & post a diagram(eventually).

BTW,
This is in the basement of a restaurant.
Shouldn't SER cable should be prohibited?

#85594 07/21/03 08:02 AM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
If the neutral & the ground are connected to the same lug and or busbar at both ends, that is your parallel path.

There is nothing I know of in the NEC that would prohibit the use of SER cable in a restaurant, prior to the adoption of the 2002 NEC, and even then it would depend on the type of construction used and how the cable is installed. See 338.10(B)(4) and 334.10(3)


Few things are harder to put up with than the annoyance of a good example.
#85595 07/21/03 09:05 AM
Joined: Mar 2001
Posts: 2,056
R
Redsy Offline OP
Member
Tom,

A restaurant would be considered a Place of Assembly (Article 518).
Wiring methods, generally, need to be Metal Raceways or MC cable (518.4 (A)).
I guess the basement ceiling/restaurant floor could be non-fire rated? (518.4 (B)).

[This message has been edited by Redsy (edited 07-21-2003).]