#85326 06/20/03 07:15 AM
Joined: Jul 2001
Posts: 37
R
RickG Offline OP
Member
As far as the NEC goes, is it permissible to install 4/0 al service entrance conductors to a non dwelling service consisting of only 1 service disconnect? I thought that the minimum was 250 MCM al for this type of service. So many electricians seem to think that 4/0 is OK for 200 amp commercial. I am looking for other opinions & code references. Thanks,
Rick

Horizontal Ad
Joined: Mar 2002
Posts: 582
R
Ron Offline
Member
Table 310.15(B)(6) can only be used for dwellings. A 200A commercial service must be from table 310.16, 250 kCMIL AL minimum.


Ron
Joined: Jun 2002
Posts: 15
E
Member
4/0 Al 75deg is rated at 180A
Round 'er up to 200A.
4/0 must meet article 220 load calc.

Joined: Jan 2003
Posts: 4,391
I
Moderator
240.4(B)Allows us to round up to the next standard size breaker under 800 amps.

Before doing this read the article yourself to see if you meet the 3 requirements.

For this service you should be all set.


Bob Badger
Construction & Maintenance Electrician
Massachusetts