Joined: Jan 2002
Posts: 163
D
Member
Here is a very devisive issue - if several EGCs enter a distribution panel [or service panel], can you connect two or more of them together and pigtail a properly sized conductor to the EGC terminal bus? (e.g. 3 #12s enter the panel, you connect them together and run a #12 pigtail to the terminal).

The 2002 HEC Handbook 'commentary' for 250.122(C) says: "It [the EGC] is not required to be sized for the 'composite' of all the circuits in the raceway because it is not anticipated that all circuits will develop faults at the same time." - yes, this is a commentary on properly sizing the EGC in a j-box or conduit.

At issue: If you can size a single EGC to protect several circuits in a raceway or j-box, can you not do the same thing in the panel?

384-20 speaks of the requiring the grounding of panelboards, but it does not specifically address this question and I know of no other code section that does address this specifically.

The current language of 384-20 came into the code in 1990 and the 1990 NEC Handbook does not speak directly of this issue either.

BTW - this is NOT a practice I condone or support; however it is one of those 'code issues' I would like a clear and concise answer to. Opinions are great (mine is - don't do it), but the question is: Is there a particular code section prohibiting this practice?

Anyone have copies of the ROPs/ROCs for the 1990 code cycle?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jun 2003
Posts: 681
P
Member
Hello Dana,

Actually you have the code reference cited in your post. 99 NEC 384.20 & 2002 NEC 408.20 are the section to find it.
The second sentence... Where the panelboard is used with nonmetallic raceway or cable or where separate grounding conductors are provided, a terminal bar for the grounding conductors shall be secured inside the cabinet.

This is telling you to terminate the EGC at the terminal bar.
The NEC and the UL White Book both stipulate that if the terninal bar is not listed for more than 1 conductor in a terminal, than all conductors shall be individually terminated.

250.122(C) does not specify splicing multiple conductors, but says if you run MULTIPLE CIRCUITS, you can use '1' EGC in the raceway or cable as long as it is sized to the largest overcurrent protective device of the largest circuit in that raceway or cable.

Splicing all the EGC in a junction box is not a recomended practice if they are of different circuits.

I hope this helps

Pierre


Pierre Belarge
Joined: Mar 2003
Posts: 92
G
Member
Pierre, You have to join all EGC in the J-box per code. Also some older panels do not have enough terminals on the neutral bar and you must do as you state.

Joined: Jan 2002
Posts: 59
C
Member
408.20 requires the equipment grounding bus, and 110.3(B) tells us that lissted equipment shall be used as per any instructions in the listing. That means one wire per terminal unless two per terminal are permitted. No bundling of all equipment grounding conductors in a panelboard.
Creighton

Joined: Jan 2003
Posts: 4,391
I
Moderator
Pierre

250.148 is the article that requires all EGCs to be connected together in a j box.

There is one exception to this for isolated grounds.



[This message has been edited by iwire (edited 06-13-2003).]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Joined: Oct 2000
Posts: 2,749
Member
Quote
408.20 requires the equipment grounding bus, and 110.3(B) tells us that listed equipment shall be used as per any instructions in the listing. That means one wire per terminal unless two per terminal are permitted. No bundling of all equipment grounding conductors in a panelboard.
Creighton

Thank you Creighton!! I hope this settles this question that also asked in other areas on the net, and as stated the answer can be found in the reference that you quoted!


Joe Tedesco, NEC Consultant
Joined: Jun 2003
Posts: 681
P
Member
Hello iwire,

I do respect what everyone here has to say, so I am going to ask you a favor. Read 250.148 again, I will post it here
Quote
250.148 Continuity and Attachment of Equipment Grounding Conductors to Boxes.

Where circuit conductors are spliced within a box, or terminated on equipment within or supported by a box, any separate equipment grounding conductors associated with those circuit conductors shall be spliced or joined within the box or to the box with devices suitable for the use...


...any separate equipment grounding conductors ASSOCIATED WITH THOSE CIRCUIT CONDUCTORS

Lets say there is a 6x6 jbox and we have multiple raceways (jbox and raceways are PVC) with multiple circuits. I am pulling an EGC with each circuit. I splice the EGC's of ONE CIRCUIT together(lets say those are 12 wire for receptacles). There is another 12 wire circuit(for lighting) in the same jbox, and I splice those associated conduuctors together and send them on their merry way. If I am reading this correctly, because they are not associated circuit conductors, and not associated circuits, I am not required to splice the EGC's of that circuit together with the other circuit EGC's. How big of a splice might that be if I had to, and how would I terminate such a large splice?

Thanks, let me know what you think,

Pierre


Pierre Belarge
Joined: Jan 2003
Posts: 4,391
I
Moderator
In the area I work it is interrupted as all grounds other than IGs must tie together.

Can you explain the need for the exception for IG circuits if your interruption is accurate.

Quote
Exception: The equipment grounding conductor permitted in 250.146(D) shall not be required to be connected to the other equipment grounding conductors or to the box.

As for how I do it, if it is more than a large blue wire nut is listed for I install a ground bar.

I can see your point if pulling separate grounds for each circuit and some circuits pass straight through with out splices I would not interrupt them at the box.

Most times in raceway we run one grounding conductor as allowed by 250.122(C) so I would have to land at each box with splices.

What do you think about a residential metal switch box with 2 or more circuits in it, how would you deal with the grounds here.

I am here to learn too, so if I am wrong straighten me out. [Linked Image]

Bob


[This message has been edited by iwire (edited 06-14-2003).]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Joined: Nov 2000
Posts: 2,148
R
Member
Joe,
I don't see any wording in the cited section that would prohibit this practice. It doesn't say that each EGC must be directly connected to an equipment grounding terminal. I don't like this idea, but still don't see any code rule that will prevent it.
Don


Don(resqcapt19)
Joined: Jun 2003
Posts: 681
P
Member
Hello Bob


This is good, we can hash this out, and be able to help each other out here.

About the exception: I believe this exception is trying to deal with 250.148, in a sense as to the extent that the IG is not required to be connected to the EGC, for obvious reasons, that I know you know.(that was hard for me to put in words, if it does not make sense to you, I will try to put it in other words, let me know)

I am not at all against using a ground bar, in a large enough jbox, and actually have, if you do want to connect them all together.
BTW - I am not against connecting All the EGC together, I just do not think this section is making it required.

I also run 1 EGC in a raceway sometimes when the bidding process makes that necessary, But... if I can I like to run individual EGC's

In a metal residential switch box I would probably splice them all together, only because there probably will not be too many.

Not trying to be a pain, but answering how I would do it, so as to see what you would do.

Pierre


Pierre Belarge