#8420 03/20/02 09:00 PM
Joined: Dec 2001
Posts: 201
A
ayrton Offline OP
Member
I need to size my breaker in the MDP for an HVAC installation. There will be four ten ton split system units. Two on one floor and two on the floor above. the condensors will be roof top. 208/120 3phase is the system.
Now this is to be on the third and fourth floor. I am planning to run conduit up from the substation in the basement to a sub panel on the third floor to feed the new units. How do I calculate for my breaker size to the subpanel?

Horizontal Ad
#8421 03/20/02 09:06 PM
Joined: Dec 2000
Posts: 4,295
Member
Largest unit @ 125% + the remainder of the units @ 100%,just like a bank of motors. If the evap coils are on this panel also, don't forget 'em.
(OOPS, that was for the conductor size!!) [Linked Image]



[This message has been edited by electure (edited 03-20-2002).]

#8422 03/20/02 10:50 PM
Joined: Mar 2001
Posts: 2,056
R
Member
I'm thinking for Inverse Time CBs, per Art. 430.62 and table 430-52--
250% largest FLA, plus sum of all other FLAs.

I don't imagine a compressor of that size is hermetic, but in that case, 440-22 would apply.

If I'm wrong, I think it's a step in the right direction.

#8423 03/27/02 06:00 PM
Joined: Mar 2002
Posts: 29
D
Member
I believe Redsy is correct. Size the feeder circuit breaker at not more than:

- Largest motor FLA (per Table 430.52) X 250% (or the next standard size up)

plus,

- The full-load current of all other motors.

An additional consideration that I would recommend is to add a fusible disconnect at the HVAC unit. This provides a local disconnect for the unit to facilitate maintenance requirements and also may be needed if the unit requires protection from fuses...applying products according to their listing and labeling - NEC 110.3(B).

Some HVAC units indicate max overcurrent device, which can be protected by a fuse or circuit breaker. In this case a non-fused disconnect would work as the local disconnect(provided the fault current is not above 10kA, since most non-fused disconnects are not rated above that).

However, many indicate max fuse size. If this is indicated, fuse protection in accordance with the label must be provided. Many engineers I talk with always specify a fused disconnect at the HVAC for this reason.

#8424 03/27/02 06:25 PM
Joined: Dec 2001
Posts: 201
A
ayrton Offline OP
Member
Thanks for the help guys. After I wrote the question I went looking in Articles 430 and got confused. There is so much information and sometimes I read to much into the text.
You have LRA, and FLA. Which do you go by?
Figuring one unit is easy, you just look at the name plate and the max fuse is normally a given. I am terrible at calculations and am always second guessing myself. Last thing I want to do is bid a job, do it and than down the road come to find out my calc was wrong!
Thanks again for the advise! Turns out I will need a 400a subpanel to handle these loads and some small 120v control.

#8425 03/31/02 12:07 PM
Joined: Apr 2001
Posts: 507
G
Member
message deleted

[This message has been edited by golf junkie (edited 03-31-2002).]

#8426 03/31/02 05:35 PM
Joined: Feb 2002
Posts: 33
J
Member
Another thing, there are HVAC rated breakers as opposed to regular ones and of course time delay fuses. As a HVAC tech I strongly suggest a dissconnect at each of the units, I would think it to be required.

As for LRA and FLA, one is Locked Rotor Amps and the other is Full Load Amps, I would think LRA to be used in calc since the compressors will draw it for a second or two, right?

Horizontal Ad
#8427 03/31/02 10:26 PM
Joined: Oct 2001
Posts: 135
W
Member
Hello JohnnyB, Didn't expect to run into you here.

#8428 04/01/02 07:20 AM
Joined: Mar 2001
Posts: 2,056
R
Member
JohnnyB,
It's early, and I'm goin' out on a limb but,
I believe FLA is normally used to size feeders & feeder OCPDs.
I believe LRA is used to size discos for hermetic units by using Table 430-151(B) to back-calculate for a HP rating based on LRA.
Anyone else?

#8429 04/01/02 08:40 AM
Joined: Mar 2002
Posts: 31
S
Member
Right on, Redsy. Won't anyone cut your limb for that.


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
AllClear
AllClear
Belmond Iowa US
Posts: 44
Joined: August 2005
Top Posters(30 Days)
Popular Topics(Views)
338,449 Are you busy
263,861 Re: Forum
244,181 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5