ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 205 guests, and 28 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#83094 01/09/03 08:47 PM
Joined: Jan 2003
Posts: 1
T
Tom jr Offline OP
Junior Member
I have not been able to get an answer i can understand to my electrical question about line volt. thermostats. The honeywell t451 has proven itself to be a very unreliable stat. So i bought 6 t498 electric heat thermostats and installed them at 6 different houses. They are working well, with no call backs. Before i install more i called honeywell to ask if this was ok to do?The answer they gave me was that the t451 is a "conductive" stat. & the t498 is a "resistive" stat. there for the 498 should not be used on oil hot water system. The lady i spoke to on the Honeywell tech. support line could explain further. Before i purchase any more and get myself in trouble what do you think.
Thank You in advance,
From Tom jr

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jul 2002
Posts: 175
E
Member
Tom, I think they probably meant inductive, not conductive.
Inductive loads, involving motors, transformers, and relay coils, causes more arcing and require contacts that will withstand the increased wear.

Electric heat is a resistive load.

Ed

Joined: Oct 2001
Posts: 597
E
Member
Tom,

I think Ed nailed it. The T498 has a rating of 22A noninductive (resistive), and nothing is listed about inductive load.

The T451 shows up in a '89 catalog and has an inductive rating of 4A Full Load @ 208/240/277, 24A Locked Rotor, and 7.2A resistive.

Ah, the difference a decade makes.

Al