#82836 12/19/02 12:26 AM
[Linked Image from users.stargate.net]
I'm having trouble coming up with a plan to provide enough receptacles to this kitchen island to meet code.
The ends shoud be okay and will probably need two at each end, but there is an area in the center that would need a receptacle as well.
The dimensions are: 5' deep by 6'6" wide.
Adjacent to the sink is a compactor (to the left of the sink), and a dishwasher (to the right).
The more I think about it, the more receptacles this thing is gonna need!
Help!
Any ideas?
[This message has been edited by sparky66wv (edited 12-18-2002).]
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Stay up to Code with the Latest NEC:
>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep
>> 2020 NEC & Related Reference & Study Guides
#82837 12/19/02 12:44 AM
Virgil
Only one receptacle is required for an Island counter with a long dimension of 24" or greater in length and a short dimension of 12" or greater. Since there this a sink in the middle of your island it will probably be considered 2 counter spaces so 1 receptacle on each end would be sufficient.
Curt
Curt Swartz
#82838 12/19/02 01:30 AM
It appears that only 1 recept is needed on an island.
#82839 12/19/02 01:57 AM
Virgil,
Relax, Breathe ...
Look at 210.52(C)(2) and 210.52(C)(4)
#82840 12/19/02 05:55 AM
Virgil:
Did you create that image?
#82841 12/19/02 08:24 AM
Only one is needed on that island. Install one one the side and you are fine. I (succesfully?) argue that only one is needed because that is one "island counter space". Even with the sink the two ends are not really separated the way the counter extends accross behind the sink. Most inspectors around here would agree and common sense would prevail.
[This message has been edited by Electricmanscott (edited 12-19-2002).]
#82842 12/19/02 12:04 PM
Doh!
Y'know, I rarely have to deal with these dern things!
One on each end will do it!
Whew!
TG, 3D Home Architect Deluxe 3.0 ...
As mentioned in another thread, its got some bugs, but does a fine job for the things I use it for!
[This message has been edited by sparky66wv (edited 12-19-2002).]
-Virgil
5 Star Inspections
Member IAEI
#82843 12/19/02 05:22 PM
I think one on the island would do it.
#82844 12/19/02 06:01 PM
E-Scott,
I'll bid for two and install one... (Just in case)...
-Virgil
5 Star Inspections
Member IAEI
#82845 12/20/02 10:58 AM
Thanks, Virgil.