ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 260 guests, and 19 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#82276 10/30/02 11:28 PM
Joined: Oct 2000
Posts: 3,682
Likes: 3
Admin Offline OP
Administrator
Member
Quote
In the NEC 1999, Art. 351, A, 351-23, B(not-permitted), (3) state that Sealtight length no longer then 6 feet, except by Section 351-23(a)(5).

In our Chemical Plant, ours T-stan used to state that the recommended length was 36" long, minimum 12", maximum 6 foot, anything longer had to have Departmental approval. Our company like most company have started following the NEC and stop using the T-stan, now here where my concern come in.

In NEC 2002, page 70-193 (soft-cover) under Liquid tight Art. 350, 350.12 show Uses Not Permitted, that the length have been taken out. Since ours plant and other are following the NEC, I feel like this can have some serious consequences. I have already seem 20 foot section of flex ran in the feel in Class 1, Div 1 & Div 2 areas. I have talk to ours Electrical Engineers, Electrical people and others, and they say that we need to go by the old standard, but since their is no official documentation, beside the NEC, that technically, contractor or others can run what ever they want. I was just involve in a Explosion last December, I believe this is a risk that isn't worth taking.

Please let me know what you think about my concern and why, so I can share it with ours staff. Thanks.

Jackie R Jennings

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Oct 2002
Posts: 3
E
Junior Member
The 6ft rule is for grounding purpose. only,if you install a grounding conductor their is no limit to how long it maybe


EdMat
Joined: Mar 2001
Posts: 2,056
R
Member
'99 351-23(b) refers to non-metallic sealtite, or LFNC. This in now in Art 366.12, and the 6' limitation does remain, with the previous exceptions.
As far as Hazardous Locations, I don't see LFNC permitted in either Div.1 or 2.
Are you sure you're not seeing the installation of MC-HL cable? It looks like sealtite, but is approved for Hazardous Locations.

Joined: May 2003
Posts: 1
J
Junior Member
I'm sorry I haven't reply, I sent a note to the NEC and was waiting for a reply. Sorry. One of my concern is on longer lenght, we have ended up with water in the flex and are having shorted wiring in long runs. This is extremely dangerous in a Div 1 area, can be bad in a Div 2 area. Our Flex has the metal rib inside, this isn't plastic flex. I would appreciate any reply witha referance so I can share with my folks. Here is the type of flex we used. Thanks.
CONDUIT, LIQUID TITE SEALTITE, TYPE UL
ULTRA TITE TYPE EF, 1/2"
(100 FT/PKG

Joined: Nov 2000
Posts: 2,148
R
Member
Jackie,
There never has been a general 6' length restriction on the use of liquidtight flexible metal conduit as long as it is securely fastened every 4.5' and with in 12" of each termination and there is no more than 360° of bend between pull points. Every little up, down or side to side bend in the flex needs to be counted toward the 360° maximum. There is a restriction of using the LFMC as the equipment grounding conductor when the length is over 6', but this restriction does not prevent the use of longer lengths, it just requires you to pull an EGC in the flex.
The rules are different for the classified areas, LFMC is not permitted in Class 1 Division 1 areas. See 501.4(A). It is permitted in Class 1 Div 2 areas by 501.4(B), but only where flexibility is required. Unless the equipment moves 20', I don't see how the use of 20' lengths of LFMC in a 1-2 area is code compliant.
As far as the water in the conduit, it is almost impossible to keep out. The conductors in the conduit should be rated for wet locations and the water should not be causing any problems unless the conductors.
Don


Don(resqcapt19)