I routinely fuse #8 copper at 40 amps. Table 310-16 says #8 THHN is good for 50 amps. A customer is replacing an existing spa with a spa with a 30 amp 240 v GFI and a 20 amp 120 v GFI. The disconnect box is fed with 4#8 CU conductors from a 50 amp CB in the main panel about 90 feet away. Do I need to replace the #8 CU with #6 CU? Bob
|
|
|
|
Joined: Apr 2002
Posts: 7,381 Likes: 7
Member
|
Bob: I don't fully understand your question. Is the spa 240 volt, 3 wire (hot/hot/neut/grd) or 2 wire (hot/hot/grd)??
How does the 120 volt GFi "fit-in"?? If you "tap it off" of the 50 amp feeder, how are you protecting it?? (OCP)
The prime answer is "yes" you can protect 8 THHN Cu at 50 amps per NEC 310-16, before you do any de-rating, if required.
The above is my humble opinion. John
John
|
|
|
|
Joined: Apr 2002
Posts: 558
Member
|
Bob
#8 THHN is rated for 50 amps if all of the terminals it is connected to are rated for 75C. If the terminal are not marked with a temperature rating or only rated for 60C then #8 is only good for 40 amps so #6 would need to be used.
Curt
Curt Swartz
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
not a stupid Q at all considering the varied interactive formats for derating scattered thru the NEC
|
|
|
|
Joined: Aug 2002
Posts: 141
OP
Member
|
There is a 30 amp 2 pole (240 volt) GFI for the heating elements and a 20 amp single pole (120 volt) GFI breaker for the motor. I would be pulling 3#10 (black, red and green)wires and 2#12 (black and white) wires from the GFI breakers to the spa. I often wonder what the energy cost per hour spent using these things is. I guess ours is not to wonder why. Ours is but to make money hooking up the damn things.
|
|
|
|
Joined: Apr 2002
Posts: 7,381 Likes: 7
Member
|
Elecbob: Didn't put the derating thing in my post to you, sorry. The cost would be approx. 240x30=7200 watts 1 HP motor= 750 watts total max of 7950 watts or 8 KW rounded max At 12cents per KWHr, a whopping calculated 96 cents. Actual costs will vary based on the local utility rates, and service charges that are added to the monthly billing.
The above disclaimer is for 66wv. John