non continous ground wire #81994 10/11/02 02:43 PM
Joined: Aug 2002
Posts: 19
G
gregoryf Offline OP
Member
I just looked at a house with a 200 amp 1-Ø service. The contractor installed a #4 solid copper conductor to the rebar in the foundation. He attached the conductor to the rebar with an acorn clamp (listed for use on 5/8" ground rod.) He then attached another #4 solid copper conductor to the rebar under the same clamp and connected it to the copper water pipe.
I believe this installation is in violation of the NEC as the ground wire should be continous. I also think the connection to the rebar should be an exothermic weld (Cadweld).
What do you think?

2017 / 2014 NEC & Related Books and Study Guides
Re: non continous ground wire #81995 10/11/02 03:26 PM
Joined: Oct 2000
Posts: 5,389
S
sparky Offline
Member
I think the dude cheesed it out, a cadweld would be an improvement, and as it may be undetermined at to the rebar's integrity,( cheesy Ufer too?), a few G-rods would not hurt.

Re: non continous ground wire #81996 10/11/02 08:23 PM
Joined: Oct 2001
Posts: 30
T
Tom Baker Offline
Member
The grounding electrode conductor (GEC) has to be continuous to any available electrode.
From that point the GEC stops and a connection to any other electrode is a bonding jumper. The connection to the rebar is OK if the acorn clamp is listed for direct burial/rebar/concrete encasement.

But two conductors under one clamp is most likely a violation of 110.3(B)
While a cadweld connection may be desirable, Burndy would like you to know they make a compression connection they belive is superior. Whatever is used must be listed for the application.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
TOOL_5150
TOOL_5150
Bay Area
Posts: 61
Joined: August 2007
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 9
Popular Topics(Views)
272,005 Are you busy
205,892 Re: Forum
193,949 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3