#81734 09/15/02 07:22 AM
Joined: Sep 2002
Posts: 131
T
Member
Why are non restriceive twin breakers made if you can't use them to over fill a panel box. The only panels that can exept twins have the notch in them. What the dilio???

2017 / 2014 NEC & Related Books and Study Guides
#81735 09/15/02 10:33 AM
Joined: Apr 2002
Posts: 558
C
Member
Older load centers did not have notched stabs but many were approved for use with twin breakers in the positions shown on the wiring diagram. The problem was people were installing these breakers in any position and in panels that were not approved for twin breakers so they had to come up with a CTL design. They still make the breakers for use in older panels without the notches but usually cost quite a bit more.

Curt


Curt Swartz
#81736 09/15/02 12:46 PM
Joined: Feb 2002
Posts: 2,233
H
Member
That is one of my pet peeves. When I go on an inspection and I see twin breakers, I have to look at the wiring diagram and/or the panel model number. Some panels like the ITE (Siemans) 20-20 panel means that it can handle 20 full size breakers only. No twins. Then the contractor usually argues with me that panels can haold up to 42 circuits. Well that is true, however the manufacture of a certain panel only wants a certain number of breakers in that panel. I wish that the manufactures all had seperate configurations for their own equipment and not let everyone elses in there. It might be so much easier.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
NickD
NickD
Amish Country, PA
Posts: 46
Joined: March 2013
Top Posters(30 Days)
dsk 2
NORCAL 1
Popular Topics(Views)
286,522 Are you busy
218,952 Re: Forum
205,076 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5