I work in a factory that basicly has no GFCI in it my boss has asked me to find out what the code is on were we need to install them. we have outlets on almost every i beam throughout the plant with hard wired extension cords and some of the outlets are running next to water pipe that comes down the i beams. guys i need alittle help on this were all do we need to have GFCI's

Horizontal Ad
Joined: Nov 2000
Posts: 2,148
R
Member
Quote
210.8(B) Other Than Dwelling Units. All 125-volt, single-phase, 15- and 20-ampere receptacles installed in the locations specified in (1), (2), and (3) shall have ground-fault circuit-interrupter protection for personnel:
(1) Bathrooms
(2) Rooftops
(3) Kitchens
Per the code the above are the locations where GFCI protected receptacles are required. Of course 527.6 requires that any temporary wiring used for repair or maintenance must have GFCI protection. Extension cords are temporary wiring. So you either use portable GFCIs of install GFCI protected receptacles anywhere maintenance or repair work could be done.
Don


Don(resqcapt19)
Joined: Oct 2000
Posts: 2,749
Member
See the 2002 NEC Index:

Ground-fault circuit-interrupters
Accessory buildings, dwelling units, 210.8(A)(2)
Basements, dwelling units, unfinished, 210.8(A)(5)
Bathtubs, hydromassage, 680.71
Definition, Art. 100-I
Deicing and snow-melting equipment, 426.32
Electrically operated pool covers, 680.27(B)(2)
Fountains, 680.51(A)
Garages, commercial, 511.12
Garages, dwelling units, 210.8(A)(2)
Permitted uses, 210.8, 215.9
Personnel, protection for, 426.32
Pipeline heating, 427.27
Pools and tubs for therapeutic use, 680.62(A)
Receptacles, 210.8
Bathrooms, in dwelling units, 210.8(A)(1)
Bathrooms in other than dwelling units, 210.8(B)(1)
Boathouses, 555.19(B)
Construction sites, at, 527.6
Existing, 406.3(D)(2)
Garages, in dwelling units, 210.8(A)(2)
Health care facilities, 517.2(A)
Kitchens in dwelling units, 210.8(A)(6)
Marinas and boatyards, 555.19(B)
Mobile homes, 550.13(B), 550.32(E)
Outdoors, dwelling units, 210.8(A)(3)
Park trailers, 552.41(C)
Pools, 680.5, 680.6, 680.22, 680.23, 680.32
Recreational vehicles, 551.40(C), 551.41(C), 551.71
Required, 210.8
Rooftops in other than dwelling units, 210.8(B)(2)
Sensitive electronic equipment, 647.7(A)
Spas and hot tubs, 680.42, 680.43, 680.44, 680.57
Wet bar sinks, 210.8(A)(7)

PS: See 600.10(C) and 620.85,

[This message has been edited by Joe Tedesco (edited 09-11-2002).]


Joe Tedesco, NEC Consultant
Joined: May 2002
Posts: 202
J
Member
i saw both of the sections you guys have listed in my nec book when i was looking today. the temp wiring (extension cords) are used by everyone in the shop so that is what i thought they should be protected. When we say kitchen does that include a break area that has 3 microwaves and a fridge.

Joined: Oct 2000
Posts: 5,393
S
Member
jlhmaint,
there's really no definition of kitchen, however most may side with a food preperation area......

Joined: Oct 2000
Posts: 2,749
Member
NFPA Definition of a Kitchen.

An area designated for storage, preparation, cooking, and serving of food for members.


Joe Tedesco, NEC Consultant
Joined: Feb 2002
Posts: 2,233
H
Member
Just my 2 cents but what code book are you following? Here in NJ it is the 1999 NEC.

Horizontal Ad
Joined: Dec 2000
Posts: 218
S
Member
JLH in our plant we use GFI for all watercoolers, the rest of them are not. We also use them on extension cords.

Joined: Apr 2001
Posts: 518
J
Member
As a rule of thumb, GFI's go where ever moisture is likely to be present. Therefore, a breakroom without a sink would probably not "need" them.
Also, as a rule of thumb, GFI's might NOT be a good idea if the appliance messes up the power, by either having a motor start up against a load (refrigerator or compressor), or a large transformer (flourescent lights, battery chargers). I'd also think twice about GFI's serving equipment that invariable has some current leakage (dishwashers, garbage disposals).
GFI's are very good detectors of damaged extension cords.


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
CharlieE
CharlieE
Indianapolis
Posts: 201
Joined: April 2004
Top Posters(30 Days)
BigB 6
timmp 2
Popular Topics(Views)
329,530 Are you busy
254,376 Re: Forum
236,838 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5