#81671 09/05/02 08:58 PM
Joined: Sep 2002
Posts: 2
V
Vic S Offline OP
Junior Member
Here's the dilemna: 300-4d of the NEC requires protection of NM sheathed cable and MC cable within 1/1/4" of the edge of a stud where the conductors are LIKELY to be penetrated. The local AHJ's are requiring nail plates behind the conductors on a 3-1/2" stud wall where the non-metallic sheathed cable enters a plastic box in a typical residence. I hope you got that. In other words, not only where a cable is perpindicular to a stud and the clearance is less than 1-1/4", but also where the cable enters the box, because this space could be as little as 1/4". The inspectors are reading the intent in the 99 handbook and not the literal sense of the word. Is anybody in the country having to protect the back of a box where the cable enters it with nail plates and does anybody agree with this? Please respond to this. Florida enforces only the 1999 NEC with no exceptions in accordance with the Florida Building Code.

Horizontal Ad
#81672 09/05/02 09:39 PM
Joined: Jan 2002
Posts: 324
A
Member
I have heard some good ones, but that one will go on my top ten. What's next, RMC for residential. Gimme a break. Perhaps you might want to run some stud guards across the breakers too, just incase they decide to hang a picture there.

#81673 09/06/02 04:46 AM
Joined: Sep 2002
Posts: 2
V
Vic S Offline OP
Junior Member
Thanks for that response. Is anybody else out there? I suppose nobody else has heard that?

#81674 09/06/02 06:07 AM
Joined: Oct 2000
Posts: 5,393
S
Member
yes i've heard of it....

as a matter of fact the boxes themselves have been questioned as to being unapplicable, in lieu of 4 sq's with sidestraps....

are not a few nailplates are really a small price to pay for thier silence?

#81675 09/06/02 07:23 AM
Joined: Oct 2000
Posts: 4,158
Likes: 5
Member
Vic,

I'm here, and have wondered about this very thing myself, but have never heard of additional protection being required by anyone. Perhaps you could send the Manufacturers an email and ask them why they put the holes where they do. I think we'd all be interested in hearing the answer if you get one.

Bill


Bill

Link Copied to Clipboard
Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Advertisement:-Right
Member Spotlight
cookcc
cookcc
California ,Long Beach
Posts: 28
Joined: May 2007
Top Posters(30 Days)
Trumpy 5
dsk 1
davey 1
Popular Topics(Views)
552,969 Are you busy
427,590 Re: Forum
398,059 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5