240.4(B) when? #81517 08/24/02 01:10 PM
Joined: Apr 2002
Posts: 189
T
triple Offline OP
Member
I am uncertain as to when this section can be sited as a reason for utilizing a breaker with a rating above the ampacity of the conductors being protected. Say, for instance, the ampacity (after all derating) of a set of service conductors is 380A. Since, according to 240.6(A), standard breaker size jumps from 350 to 400A, can the conductors with an ampacity of 380A feed a 400A service?

2017 / 2014 NEC & Related Books and Study Guides
Re: 240.4(B) when? #81518 08/24/02 01:19 PM
Joined: Apr 2002
Posts: 558
C
caselec Offline
Member
The 380 amp conductors may be protected by a 400 amp over current device but the maximum calculated load on these conductors can not exceed 380 amps.


Curt Swartz
Re: 240.4(B) when? #81519 08/29/02 11:24 AM
Joined: Nov 2001
Posts: 11
S
safari Offline
Member
For service over current protection and conductor coordination you must look in services because the rules are diferent.

230.90.A

This does not allow for selection of the next higher size of over current protection.

tom

Re: 240.4(B) when? #81520 08/29/02 04:32 PM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
Rounding up to the next standard size is permitted. Take a look at 230.90(A) exception 2 and if you have the handbook, see the commentary following the exception.

Tom


Few things are harder to put up with than the annoyance of a good example.

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Lostazhell
Lostazhell
Bakersfield, CA (Originally Orange Co.)
Posts: 1,432
Joined: February 2004
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
271,012 Are you busy
205,010 Re: Forum
193,126 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3