#81517 08/24/02 12:10 PM
Joined: Apr 2002
Posts: 195
T
triple Offline OP
Member
I am uncertain as to when this section can be sited as a reason for utilizing a breaker with a rating above the ampacity of the conductors being protected. Say, for instance, the ampacity (after all derating) of a set of service conductors is 380A. Since, according to 240.6(A), standard breaker size jumps from 350 to 400A, can the conductors with an ampacity of 380A feed a 400A service?

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

#81518 08/24/02 12:19 PM
Joined: Apr 2002
Posts: 558
C
Member
The 380 amp conductors may be protected by a 400 amp over current device but the maximum calculated load on these conductors can not exceed 380 amps.


Curt Swartz
#81519 08/29/02 10:24 AM
Joined: Nov 2001
Posts: 11
S
Member
For service over current protection and conductor coordination you must look in services because the rules are diferent.

230.90.A

This does not allow for selection of the next higher size of over current protection.

tom

#81520 08/29/02 03:32 PM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
Rounding up to the next standard size is permitted. Take a look at 230.90(A) exception 2 and if you have the handbook, see the commentary following the exception.

Tom


Few things are harder to put up with than the annoyance of a good example.

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mxslick
mxslick
Atomic City, ID USA
Posts: 806
Joined: October 2004
Top Posters(30 Days)
BigB 9
triple 3
Popular Topics(Views)
302,561 Are you busy
231,910 Re: Forum
216,544 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5