From Norm Koon:

I have a question concerning cables that are approximately 45 years old.

The insulation resistance test read as follows:

Air Temp 82 deg F
One Minute Megohm readings Ph A 1220 Ph B 2540 Ph C 484
Ten Minute Megohm readings Ph A 1470 Ph B 4100 Ph C 510
PI Index Ph A 1.11 Ph B 1.61 Ph C 1.05

Given this test data, would it be advisable to reuse these cables?

These cables are partly running underground, inside a basement and outdoors, so
an accurate temperature reading was not used. The temperature is only the outside
air temperature. Also they are still hooked up to the primary bushings of the transformer.

So they are not true readings of the cables. I was wondering if the disparity of the readings could be due to leakage on the transformer bushings. The test voltage was 2500 vdc. The system voltage is 6900 volts ac.


Joe Tedesco, NEC Consultant
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#81417 08/12/02 03:21 PM
Joined: Apr 2002
Posts: 2,527
B
Moderator
"...still hooked up to the primary" should make individual readings meaningless, unless I misinterpreted something.

#81418 08/12/02 03:34 PM
Joined: Feb 2002
Posts: 182
B
Bob Offline
Member
Norm
The 2500 volt DC test does not provide an adequate check of the insulation integrity.
Is the cable in use now? I would want to Hi Pot test the cable. New 15 kv cable is tested at about 60 kv but that is not what you want on cable this old. Check with the mfg annd see if they can give you a value to test the cable.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Top Posters(30 Days)
Admin 1
Popular Topics(Views)
313,186 Are you busy
239,129 Re: Forum
222,897 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5