"...likely to become energized..." #81393 08/07/02 02:03 PM
Joined: Jul 2002
Posts: 103
J
jes Offline OP
Member
250.4 clearly states that electrical systems that are grounded shall be connected to earth in a manner that will limit the voltage imposed by lightning...
It then goes on to talk about grounding and bonding of electrical equipment and other conductive materials that are "likely to become energized".
At what point are the grounding and bonding requirements required to deal with lightning protection and not just ground faults within the electrical system?? For example, would a metal chimney extending up above the highest point of the structure require bonding?? Why or why not?? If so, how do you determine the size of the bonding conductor? Let's say the metal fireplace has a fan. #14 AWG circuit with equipment ground. Is that sufficient to withstand a lightning strike?
Just curious how others view the wording of 250.

2017 / 2014 NEC & Related Books and Study Guides
Re: "...likely to become energized..." #81394 08/07/02 03:10 PM
Joined: Nov 2000
Posts: 2,148
R
resqcapt19 Offline
Member
Lightning protection is covered by NFPA 780, the Lightning Protection Code. It is not really covered by the NEC.
Don


Don(resqcapt19)
Re: "...likely to become energized..." #81395 08/07/02 09:33 PM
Joined: Jul 2002
Posts: 103
J
jes Offline OP
Member
Don,
I am well aware of 780, nevertheless, those words ARE in the NEC, have been for YEARS. What do they really mean? Do they apply only to lightning voltages coming from the utility or source of supply?

Re: "...likely to become energized..." #81396 08/07/02 10:37 PM
Joined: Nov 2000
Posts: 2,148
R
resqcapt19 Offline
Member
In my opinion, the NEC in 250.4(A)(1) is talking about limiting the voltages on the electrical system that result from outside influences such as lightning. Note that it does use the word system in this section. The other parts of this section use the word "equipment" and for the most part also uses the words "fault clearing path". I don't see anything that requires lightning protection of the electrical equipment or other conductive equipment in the NEC.
Don


Don(resqcapt19)

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mersadrad
mersadrad
Montreal, Quebec, Canada
Posts: 28
Joined: March 2011
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
270,713 Are you busy
204,955 Re: Forum
193,058 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3