ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
diazed fuses
by annemarie1. 02/24/18 08:05 PM
Solid state relay or not
by gfretwell. 02/24/18 04:52 AM
Whirlpool Recalls KitchenAid Electric Kettles
by Admin. 02/22/18 11:35 AM
110.26
by gfretwell. 02/18/18 12:14 AM
New in the Gallery:
Housebilding DIY wiring
SE cable question
Who's Online Now
0 registered members (), 6 guests, and 12 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Grounding Electrode Conductors #81341
08/03/02 06:39 AM
08/03/02 06:39 AM
J
jes  Offline OP
Member
Joined: Jul 2002
Posts: 103
CT
4 story apartment complex built in 1995. As near as I can determine the entire structure is ONE building. There a six 800A, 120/208Y 'services' fed from utility padmounts and located in DIFFERENT parts of the building (floors and wings). Service conductors are routed to each electrical room through poured concrete encased conduits to an 800A fused switch. This then feeds the meter bank/apartment breaker group.
Now that's all pretty interesting (and I'll assume the AHJ gave the contractor permission to do that) but what I'm really concerned with is the GECs. There is one 4/0 AL run from each disconnect to the common utility space where the water main enters. The main is 4" CU and each GEC is separately clamped to the pipe as it enters. No supplemental electrodes provided. The water piping in the building is plastic after it leaves this room.
Workmanship looks good but does anyone have any comments on that lash-up??

2017 / 2014 NEC & Related Books and Study Guides
Re: Grounding Electrode Conductors #81342
08/03/02 07:37 AM
08/03/02 07:37 AM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,347
jes,
for the sake of good chat, please clarify here......
does the 4" CU H2O main go to plastic after it enters the building?
Or is the external plumbing plastic, and go to CU on entry?
Is this a municipal H2O main?, intergral to other buildings in close proximity ( especially of the X-former) ?
[Linked Image]

Re: Grounding Electrode Conductors #81343
08/03/02 08:16 AM
08/03/02 08:16 AM
J
jes  Offline OP
Member
Joined: Jul 2002
Posts: 103
CT
Good Morning Sparkster!
OK, the copper line is the municipal supply and is continuous underground as far as I know. The change to plastic occurs on the building side of the GEC connections (about 18" of copper before the changeover)and the building plumbing is for the most part plastic. The padmounts are on the back side of the building - opposite of the street with the watermain. There is also a metal sprinkler riser in the same room that is not bonded (which needs to be) but that doesn't change the basic question about the GEC connections.
There are other buildings across the street but we're talking 75-100 ft or so in all directions. HV to the 2 padmounts comes in from the street underground.

By the way, the 4/0 AL GEC is OK size-wize for the service conductors.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
noderaser
noderaser
Portland, Oregon, United States
Posts: 404
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
Admin 9
BigB 4
Popular Topics(Views)
244,079 Are you busy
181,084 Re: Forum
171,320 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.011s Queries: 14 (0.003s) Memory: 0.9505 MB (Peak: 1.0742 MB) Zlib enabled. Server Time: 2018-02-25 13:33:49 UTC