Senerio: Contractor does a 100 amp to 200 amp service upgrade to a single family home. The meter, and 100 amp panel, were located in the basement. The new meter is now located outside of the garage,and a new 200 amp panel is located on the inside wall of the garage. The old panel was left in the basement as a subpanel. The contractor fed the old panel with pvc from the new 200 amp panel. In the pvc are the two ungrounged legs, the neutral,and the main grounding electrode/equipment grounding conductor(one wire which hits a lug on the ground bar{neutral is isolated} then proceeds through the panel to the water meter located a couple feet away).Here's my question. Can the main g.e.c also be used as a e.g.c? I know system grounding is different then equipment grounding, but besides by definition is there an applicible article in the code I can refer to?

Horizontal Ad
Joined: Oct 2000
Posts: 5,393
S
Member
cthusky,
if in fact, this is a detatched garage, then both structures would require a GEC, and GE's, and the conductor you mention bettween panels would merely be the EGC.

Joined: Feb 2002
Posts: 6
C
cthusky Offline OP
Junior Member
Sparky, no this is an attached garage.

Joined: Feb 2001
Posts: 308
S
Member
I don't believe anything in the NEC says this can't be done. Just have to make sure you are not setting up parallel neutral paths with incorrect bonding in the sub panel.

Joined: Nov 2000
Posts: 2,148
R
Member
As long as the grounding electrode conductor is continuous and the grounded conductor is not bonded to the grounding conductor, I see no problem with the installation.
Don


Don(resqcapt19)

Link Copied to Clipboard
Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Advertisement:-Right
Member Spotlight
Posts: 362
Joined: April 2003
Top Posters(30 Days)
Trumpy 5
davey 1
se ?>
Popular Topics(Views)
552,920 Are you busy
427,513 Re: Forum
397,986 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5