Main G.E.C used also as an E.G.C #81253
07/29/02 07:45 PM
07/29/02 07:45 PM
C
cthusky  Offline OP
Junior Member
Joined: Feb 2002
Posts: 6
South Windham Ct, USA
Senerio: Contractor does a 100 amp to 200 amp service upgrade to a single family home. The meter, and 100 amp panel, were located in the basement. The new meter is now located outside of the garage,and a new 200 amp panel is located on the inside wall of the garage. The old panel was left in the basement as a subpanel. The contractor fed the old panel with pvc from the new 200 amp panel. In the pvc are the two ungrounged legs, the neutral,and the main grounding electrode/equipment grounding conductor(one wire which hits a lug on the ground bar{neutral is isolated} then proceeds through the panel to the water meter located a couple feet away).Here's my question. Can the main g.e.c also be used as a e.g.c? I know system grounding is different then equipment grounding, but besides by definition is there an applicible article in the code I can refer to?

2017 / 2014 NEC & Related Books and Study Guides
Re: Main G.E.C used also as an E.G.C #81254
07/30/02 06:16 AM
07/30/02 06:16 AM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,372
cthusky,
if in fact, this is a detatched garage, then both structures would require a GEC, and GE's, and the conductor you mention bettween panels would merely be the EGC.

Re: Main G.E.C used also as an E.G.C #81255
07/30/02 07:32 PM
07/30/02 07:32 PM
C
cthusky  Offline OP
Junior Member
Joined: Feb 2002
Posts: 6
South Windham Ct, USA
Sparky, no this is an attached garage.

Re: Main G.E.C used also as an E.G.C #81256
07/31/02 01:08 AM
07/31/02 01:08 AM
S
Steve T  Offline
Member
Joined: Feb 2001
Posts: 306
Oak Park, IL, USA
I don't believe anything in the NEC says this can't be done. Just have to make sure you are not setting up parallel neutral paths with incorrect bonding in the sub panel.

Re: Main G.E.C used also as an E.G.C #81257
08/01/02 05:25 PM
08/01/02 05:25 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
As long as the grounding electrode conductor is continuous and the grounded conductor is not bonded to the grounding conductor, I see no problem with the installation.
Don


Don(resqcapt19)

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Joe Tedesco
Joe Tedesco
Boston, Massachusetts USA
Posts: 2,749
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Admin 2
Khombo 2
Popular Topics(Views)
255,871 Are you busy
191,841 Re: Forum
181,610 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.016s Queries: 14 (0.003s) Memory: 0.9681 MB (Peak: 1.1053 MB) Zlib enabled. Server Time: 2019-06-25 23:54:40 UTC