Article 400 - Rubber Cords #81062
06/29/02 09:21 PM
06/29/02 09:21 PM
M
MVillines  Offline OP
Member
Joined: Jan 2002
Posts: 21
Henderson
Please give me your thoughts regarding the use of a rubber cord connected directly the (standby) terminals of a transfer switch (suitable for service equipment) with a male plug attached to the other end of this cord. This cord is also routed trough a section of flexible conduit that is a little shorter in length that the cord so that the plug can be attached to the cord. The electricians reasoning for the flexible conduit is to protect the rubber cord from UV rays. This cord is plugged into a generator that is mounted on a trailer next to the (Fire Station) building for standby purposes or hanging on the building if the generator is relocated. The focus of this question is the rubber cord and assuming all other is compliant.

2017 / 2014 NEC & Related Books and Study Guides
Re: Article 400 - Rubber Cords #81063
06/29/02 10:11 PM
06/29/02 10:11 PM
B
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
You probably want something like SEOW cord—sunlight resistant, wet-rated, flexible at cold temperatures, and generally suitable for use outdoors. Related article: http://www.nmsu.edu/~tdi/cc66.pdf

The trailer-mounted generator set may need a receptacle and cover that is for “wet location while in use.”

A 3R hinged-cover can nippled to the transfer switch for not-in-use storage of supply cord has worked well for me. It's likely someone has to approach the set for startup and shutdown anyway.

{The flex seems like a misapplication—I don't think it could effectively protect the supply cord from sunlight deterioration. IMO, a sunlight-resistant grade is mandated for the duty at hand.

**Reply text is intended for recreationally hallucinogenic use only.**


 


[This message has been edited by Bjarney (edited 06-29-2002).]


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Joe Tedesco
Joe Tedesco
Boston, Massachusetts USA
Posts: 2,749
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Admin 2
Khombo 2
Popular Topics(Views)
255,871 Are you busy
191,841 Re: Forum
181,610 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.015s Queries: 14 (0.004s) Memory: 0.9441 MB (Peak: 1.0576 MB) Zlib enabled. Server Time: 2019-06-26 00:13:22 UTC