#81054 06/21/02 01:57 AM
Joined: Jun 2002
Posts: 6
R
ravin Offline OP
Junior Member
Hello, I installed and elec. service with the meter can and panel practically back to back within the same partion, I used SE cable due to the meter elevation to panel knock outs not in line with each other; the inspection failed due the inspectors reasoning that since the cable is unfused, it can't be inside a partion. Builder had to build out into room a deeper wall to facilitate the use of PVC conduit in lieu of SE cable. Should I have challanged his ruling. Any thoughts on this Thank you.

Horizontal Ad
#81055 06/21/02 08:53 AM
Joined: May 2001
Posts: 717
G
Member
Ravin,
230-70(a) says it shall be installed as near as practicable. That is the only thing the NEC says on the subject, which leaves distances up to local interpretation.

In VA each county is allowed to set that distance, most of them pick 7 feet. If it is back to back (or nearly so, as you indicate) it would be allowed here. BUT you may not be here [Linked Image]

Suggest you call your local chief electrical inspector to ask what the interpretation is, an how far you're allowed to enter the building. This is an old argument, and I'm guessing they've already addressed it.

Personally, I don't think there is much 'structural' difference between the pvc and the sec.

#81056 06/21/02 08:27 PM
Joined: Oct 2000
Posts: 4,132
Likes: 4
Member
ravin,

Is this a 2x4 studded wall?

What you describe is common practice around here, but in reality there is not much to protect that cable and rather impossible to keep larger SE cables a safe distance away from finished surfaces in a 2x4 wall. It wouldn't surprise me if that was what they are concerned about. Just a guess.

Bill


Bill
#81057 06/23/02 12:30 AM
Joined: Jun 2002
Posts: 6
R
ravin Offline OP
Junior Member
No Bill, the wall is 2x6, I've done many that way also; seems this inspection was based on what ifs. Thanks for response.

#81058 07/01/02 11:53 PM
Joined: Jun 2001
Posts: 196
C
Member
se cable to the next full stud bay, or even the first full stud bay around a corner, would be acceptable here in oregon.....

when you say "same partion," i assume you mean "same partition," and assume you are refering to the "same stud bay" within a partition? which would be way ok here


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
JoeKP
JoeKP
Berkley, MA
Posts: 144
Joined: March 2008
Top Posters(30 Days)
BigB 4
Popular Topics(Views)
327,660 Are you busy
252,535 Re: Forum
235,157 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5