SE cable? #81054
06/21/02 12:57 AM
06/21/02 12:57 AM
R
ravin  Offline OP
Junior Member
Joined: Jun 2002
Posts: 6
Hello, I installed and elec. service with the meter can and panel practically back to back within the same partion, I used SE cable due to the meter elevation to panel knock outs not in line with each other; the inspection failed due the inspectors reasoning that since the cable is unfused, it can't be inside a partion. Builder had to build out into room a deeper wall to facilitate the use of PVC conduit in lieu of SE cable. Should I have challanged his ruling. Any thoughts on this Thank you.

2017 / 2014 NEC & Related Books and Study Guides
Re: SE cable? #81055
06/21/02 07:53 AM
06/21/02 07:53 AM
G
George Corron  Offline
Member
Joined: May 2001
Posts: 717
Lorton, Va USA
Ravin,
230-70(a) says it shall be installed as near as practicable. That is the only thing the NEC says on the subject, which leaves distances up to local interpretation.

In VA each county is allowed to set that distance, most of them pick 7 feet. If it is back to back (or nearly so, as you indicate) it would be allowed here. BUT you may not be here [Linked Image]

Suggest you call your local chief electrical inspector to ask what the interpretation is, an how far you're allowed to enter the building. This is an old argument, and I'm guessing they've already addressed it.

Personally, I don't think there is much 'structural' difference between the pvc and the sec.

Re: SE cable? #81056
06/21/02 07:27 PM
06/21/02 07:27 PM
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,903
NY, USA
ravin,

Is this a 2x4 studded wall?

What you describe is common practice around here, but in reality there is not much to protect that cable and rather impossible to keep larger SE cables a safe distance away from finished surfaces in a 2x4 wall. It wouldn't surprise me if that was what they are concerned about. Just a guess.

Bill

Re: SE cable? #81057
06/22/02 11:30 PM
06/22/02 11:30 PM
R
ravin  Offline OP
Junior Member
Joined: Jun 2002
Posts: 6
No Bill, the wall is 2x6, I've done many that way also; seems this inspection was based on what ifs. Thanks for response.

Re: SE cable? #81058
07/01/02 10:53 PM
07/01/02 10:53 PM
C
Cindy  Offline
Member
Joined: Jun 2001
Posts: 196
PDX, OR, US
se cable to the next full stud bay, or even the first full stud bay around a corner, would be acceptable here in oregon.....

when you say "same partion," i assume you mean "same partition," and assume you are refering to the "same stud bay" within a partition? which would be way ok here


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
MarkC10
MarkC10
CA, Inland Empire
Posts: 43
Joined: September 2013
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
252,125 Are you busy
189,137 Re: Forum
178,806 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.022s Queries: 14 (0.003s) Memory: 0.9680 MB (Peak: 1.1080 MB) Zlib enabled. Server Time: 2018-12-10 11:22:29 UTC