Swimming pool installation #81010
06/15/02 10:22 PM
06/15/02 10:22 PM
R
Redsy  Offline OP
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Twice in 2 days I have been told by 2 different people that a pool needs a ground rod. I don't see it anywhere in 680.
What gives?
And...
It is OK to reduce the burial depth to 12" for PVC conduit on a 120 volt, 20 amp filter pump if GFCI protection is ahead of the run. Correct?

[This message has been edited by Redsy (edited 06-15-2002).]

2017 / 2014 NEC & Related Books and Study Guides
Re: Swimming pool installation #81011
06/16/02 01:53 AM
06/16/02 01:53 AM
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,890
NY, USA
Redsy,

I have not heard of a Ground Rod being required. Maybe it is a local requirement?

Table 300.5 Column 4 says that 12 inches of cover is adequate for Residential applications under these conditions.

Bill

Re: Swimming pool installation #81012
06/16/02 05:18 AM
06/16/02 05:18 AM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,346
would'nt a rod or two establish a better gradient?

Re: Swimming pool installation #81013
06/16/02 12:51 PM
06/16/02 12:51 PM
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,890
NY, USA
Sparky,

I was wondering the same thing myself, especially in situations where there are no metal components to bond to. I have not heard of it being required anywhere though.

Bill

Re: Swimming pool installation #81014
06/16/02 01:41 PM
06/16/02 01:41 PM
A
arseegee  Offline
Member
Joined: Jan 2002
Posts: 324
Statesboro, GA USA
Redsy, we are required to drive a rod by our inspector. It connects the pool grid, rod and motors with one solid egc. Never questioned it but never seen the NEC require it either.

Bill, from my experience I have never seen a pool (in-ground) that didn't have something to bond. Lights and ladders of course but the concrete rebar and mesh require it too.

Re: Swimming pool installation #81015
06/16/02 02:43 PM
06/16/02 02:43 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
The object of the required pool bonding it to create an equal potential between all conductive objects in and near the pool. Installing ground rods will have no effect. They are not required by the code. In some rare cases with high earth current flow (caused by an open neutral on the utility high voltage URD cable) the addition of ground rods could possibly increase the hazard.
Don


Don(resqcapt19)
Re: Swimming pool installation #81016
06/16/02 02:49 PM
06/16/02 02:49 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,346
Don,
that's an interesting twist from our 'more is better' grounding mentality, can you expand a tad?

Re: Swimming pool installation #81017
06/16/02 06:31 PM
06/16/02 06:31 PM
H
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
I have never seen a second ground rod needed for a pool. Why the rebar that is grounded in the pool should be a great grounding electrode, right? ( If it is an inground pool with rebar.)
Harold

Re: Swimming pool installation #81018
06/16/02 06:39 PM
06/16/02 06:39 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Sparky,
It would take a number of things to happen to create a problem, but it is possible. With current flow through the earth, and ground rods in the path of this current, we make the pool equipment and water part of the current carrying path for this current. If the bonding isn't perfect, we then have a difference of potential within the pool space. Without the ground rods there would be less of this earth current flowing through the bonded system. If the bonding is 100% perfect, it won't make any difference as the people in the pool would not be exposed to any potential differences. It would be like the bird on the wire, but with problems in the bonding and earth current flow and the water we could have a problem. The earth current would be flowing in the water as a result of the bonding problem. The person in the water is a better conductor than is the water itself, so the person becomes a shunt and more current will flow on the person than the water. Yes, this would be somewhat rare, but it is not unheard of. There have been some cases reported when people in pools have been shocked because of open utility underground neutrals in the area. The fact that the primary and secondary neutrals are bonded together, makes this problem worse. With primary/secondary neutral bond and an open primary neutral, we will always have current flow through the pool as a result of the bonding connection to the pool pump EGC. Additional ground rods could make this problem worse. Maybe the best installation would be to require isolation transformers, double insulated equipment, nonmetallic pool piping, and no EGC for pool systems. Pool area bonding would still be required to keep the pool and associated equipment at an equal potential.
Don


Don(resqcapt19)
Re: Swimming pool installation #81019
06/16/02 07:14 PM
06/16/02 07:14 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,346
Don,
thanks for the rationale, and conjecture re; isolation..
this explains pool bonding as seen from external influence well....do you suppose a fault or leak to ground from the serving residence would seek to make way thru the motor EGC in the same manner??

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
noderaser
noderaser
Portland, Oregon, United States
Posts: 404
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
Admin 9
Popular Topics(Views)
244,062 Are you busy
181,052 Re: Forum
171,293 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.018s Queries: 15 (0.003s) Memory: 1.0237 MB (Peak: 1.2005 MB) Zlib enabled. Server Time: 2018-02-23 06:31:19 UTC