ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 228 guests, and 10 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 2 of 2 1 2
Joined: Feb 2002
Posts: 2,233
H
Member
What if? There were two seperate circuits for say, 4 receptacles in the kitchen for the counter top. Now say, one of the circuits goes over to a receptacle in the dining room. Would that be OK?

Harold

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Oct 2000
Posts: 5,392
S
Member
fine, 210.52(B)(1)
Kitchens,Pantry,Breakfast room,Dining room, or similar area


so...this would have to include my workvan right??...

hey, maybe this guy knows....?
[Linked Image from citypaper.com]

Joined: Feb 2002
Posts: 375
G
Member
I am not an electrictian, but I do have a coppy of the 1999 ICC 1&2 family dwelling code.

Section 4401.5.6:

"Other receptical outlets provided in the rooms and areas specified shall be provided by the small appliance branch circuits or other branch circuits."

I suspect that is taken directly from the NEC. If so, then the "other branch circuits" can have lights on them.

Joined: Nov 2000
Posts: 2,148
R
Member
George,
That is not what the NEC says. The NEC requires all of the receptacle outlets in these rooms to be on the 2 or more small applinace branch ciruits.
Don


Don(resqcapt19)
Joined: Nov 2001
Posts: 11
S
Member
ICC one and two family 4401.4 states that the two or more small appliance circuits SHALL serve ALL receptacles in thees areas and have no other outlets I believe that this is very clear.
tom

Joined: Feb 2002
Posts: 375
G
Member
Certainly 4401.4 is clear in not allowing other branch circuits. Thus, there are no "other branch circuits" for 4401.5.6 to consider.

Joined: Nov 2001
Posts: 280
M
Member
Et All:
It has always been my unnerstanding that the small appliance circuits are to be unto themselves with no other outlets before them.
I have always put the kitchen lights on the general lighting circuit and dont have these problems, leastwise so say our local inspectors.
That is a separate circuit for the kitchen lighting, problem solved.
Just my opinion, and it works for me.

-Mark-

Joined: Feb 2002
Posts: 2,233
H
Member
I have another question, How about the hood? Can that go on the kitchen circuit?

Harold

Joined: Apr 2002
Posts: 558
C
Member
The hood can go on the kitchen lighting circuit but not one of the small appliance receptacle circuits. The blowers in hoods seem to be getting bigger these days and many of them have heat lamps so often is desirable to run a dedicated circuit just for the hood.